I am a bit confused on the issue still.  I read an article about
pedestal building design in the February 06 issue of the Building Safety
Journal written by Marshall A. Klein, P.E. and David M. Hammerman, P.E.
in which they state 

"When applying Section 508.2, Item 4, only the pedestal
building is required to be sprinklered by way of Section
903.2.9 when it is an enclosed parking garage, or by
way of Section 508.2, Item 4, Exception 2, when it
contains A, B or M uses. It should be noted that if a
building above the pedestal building is required to be
sprinklered based on the sprinkler threshold requirements
of Section 903 or the height/area increase thresholds
of Chapter 5, then it must comply with the
applicable requirements of NFPA 13, Installation of
Sprinkler Systems, or, if applicable, NFPA 13R, Installation
of Sprinkler Systems in Residential Occupancies up
to and Including Four Stories in Height."  

This is based upon the 2003 IBC.  I take this to mean that
this is indeed 2 separate buildings and can be treated as such 
as far as the sprinkler system is concerned. 
How can there be such discrepancy on the issue?

Dewayne Martinez
Design Build Fire Protection
New Berlin, WI
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steve
Leyton
Sent: Friday, May 29, 2009 12:47 PM
To: [email protected]
Subject: RE: 13 & 13R - same building

Which is where your disclaimer about local AHJ's comes into play, I
presume?

Steve Leyton
Protection Design & Consulting
San Diego, CA




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of John
Drucker
Sent: Friday, May 29, 2009 8:53 AM
To: [email protected]
Subject: RE: 13 & 13R - same building

"We can debate issues of functionality, but the code clearly defines a
podium separation as separate buildings."   

However ONLY WITHIN THE CONTEXT of the referenced code section. In this
case 2006 IBC 509 et al.

"A basement and/or the first story above grade plane of a building shall
be considered as a separate and distinct building for the PURPOSE OF
DETERMINING area limitations, continuity of fire walls, limitation of
number of stories and type of construction."

As opposed to the context of 2006 IBC 705.1

"705.1 General. Each portion of a building separated by one or more fire
walls that comply with the provisions of this section shall be
considered a separate building."  

Theres a significant distinction which is being overlooked.

John Drucker


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steve
Leyton
Sent: Friday, May 29, 2009 10:51 AM
To: [email protected]
Subject: RE: 13 & 13R - same building

We can debate issues of functionality, but the code clearly defines a
podium separation as separate buildings.   If the deck is solid
reinforced concrete, and the openings are shafted or protected (3 hr.
fire stops), then you can build down to Type V above a Type 1.   Of
course, this also allows a LOT of unprotected openings at the exterior
walls above (presuming adequate setbacks), but the presumption is that
sprinklers will control  a fire below that deck and limit exterior
spread.

Steve Leyton
Protection Design & Consulting
San Diego, CA




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of John
Drucker
Sent: Thursday, May 28, 2009 9:58 AM
To: [email protected]
Subject: RE: 13 & 13R - same building

Steve & Roland,

Being that two solutions separate buildings, open space and firewalls, a
horizontal separation will never satisfy either. Whomever coined the
term "horizontal firewall" most likely wasn't using it in the context of
gravity.
So I guess it applies to the space station. Then again can one use a 13R
for the space station ?, sounds like a mixed use.

John Drucker

PS, George, Let's not start on what's being allowed by AHJ's. Also don't
feel you're alone on "combination sensing lines".  Just had one from a
licensed contractor. It has since been abated.



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steve
Leyton
Sent: Thursday, May 28, 2009 11:51 AM
To: [email protected]
Subject: RE: 13 & 13R - same building

And it should be added that the TC has proposed new language for scope
section 1.1 of 13R that, if it passes the hearing in two weeks, will
clarify that the intent is for 13R to be applied only to buildings that
are classified as residential and the ancillary occupancies within.   So
if a structure is separated horizontally or vertically into separate
buildings as defined by the code, you can have two designs - 13 and 13R
- in each separated building.   But if a structure is one building of
mixed occupancies, then it's a 13 design, period.

The foregoing is my opinion only and does not necessarily represent the
opinion or intent of the NFPA 13D/13R Technical Committee on Residential
Sprinkler Systems.

Steve Leyton
Protection Design & Consulting
San Diego, CA



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Roland
Huggins
Sent: Thursday, May 28, 2009 7:42 AM
To: [email protected]
Subject: Re: 13 & 13R - same building

even the scope of 13R and annex material confirm you can not mix the two
systems in one building.  As for HORIZONTAL separation equal to building
separation -as soon as it's possible to have the floor collapse and not
affect the other side, then we'll talk about horizontal separation for
two buildings.

Todd - who spec'd it and where does your PE status enter the issue for
incorrect application of standards?

Roland

On May 28, 2009, at 6:19 AM, John Drucker wrote:

> George,
>
> Careful George don't give em any ideas;  "If they resist you pointing 
> out the fact that 13 should apply to the entire building, maybe point 
> out that using their logic, you could do the top 4 floors of a 
> residential high-rise using 13R?"
>
> This would NOT be permitted since a high-rise would be at least 75ft 
> highest occupiable floor above lowest FD vehicle access, or appx a 6-7

> story building wherein 13R is limited to "Residential Occupancies up 
> to including four stories in height". Height being measured from grade

> plane.
>
> Guys the title and scope of the standard make it clear 13R is not 
> intended for "Residential Occupancies" and not "Mixed Use"
> occupancies.
> Common areas including private garages; mail, trash, laundry, exercise

> and storage areas that serve the residential occupancy are considered 
> "incidental" and appropriately addressed in 13R wherein these spaces 
> are designed and installed in according to 13. However in the end its 
> still a 13R system and not a 13/13R which simply doesn't exist.  Mixed

> use Buildings are provided for at IBC 508.
>
> Lastly be careful of the IBC Section 509.2 provisions. Read the 
> section carefully especially the part; "separate and distinct building

> for the purpose of determining area limitations, continuity of fire 
> walls, limitation of number of stories, and type of construction"
> There's no mention of height with regards to fire sprinkler systems 
> thus the measurement is from grade plane and not the pedestal. I'm 
> certain we have many a 5 story building out there with 13R systems.
>
> John Drucker

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 4112 (20090528) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 4112 (20090528) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 4114 (20090528) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or
entity to which it is addressed and may contain information that is
privileged and confidential, nor is it, unless specifically stated,
intended to be relied upon by any person or persons other than the
individual or entity named above and no warranties or representations
are made or intended to persons or entities not named above.  If the
reader is not the intended recipient, you are hereby notified that any
dissemination, distribution or copying of this communication is strictly
prohibited.  If you have received this communication in error, please
notify us immediately by telephone, return this message to the address
above and delete all copies.  Thank you.

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to