In a 13R building the areas outside the dwelling units are required to be designed to 13. So many confuse this and specify 13R for the residential areas and 13 for others. I find this happens very often. You need to find out if this was the intent of the specs. Personally, I'd say the building should be 13. However, it is not my call or yours.
Tony -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Todd Williams Sent: May 28, 2009 5:44 AM To: [email protected] Subject: 13 & 13R - same building I know this has been bantered around before, but I am still a little confused. I have been asked to quote a building where the 1st floor is a church and the upper 2 floors are apartments. The spec calls for the 1st floor to be 13 and the upper floors 13R. To me this doesn't make sense since 13 is a property standard and 13R is life safety. Is there any situation where this is allowed? Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut www.fpdc.com 860.535.2080 _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)