I believe that the intent was to let you know that when the occupancy exceeded 1000, more standpipe protection was required based upon that fact alone. Just as 905.3.4 allows class II & III standpipes under certain conditions for stages. Your correct there is no class three requirement in 905.3 unless its unsprinklered in which case a class I standpipe is required. But when your reading code you can't just stop because you think you've found the only thing you need. Read all of 905, see what other sections say about A occupancies, and which apply to your situation.
Is your occupancy over 1000? No? then 905.5.1 doesn't apply. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Radzicki, Michael Sent: Wednesday, June 03, 2009 11:40 AM To: [email protected] Subject: A1 and A2 Standpipes What is the intent of IFC 2006 item 905.5.1 calling out a location for Class II hose connections in the rear of auditoriums, balconies, and dressing rooms of A1 and A2 occupancies when there is no requirement for Class II systems in these occupancies in neither 905.3 nor the special detailed requirements of IBC chapter 4? _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)