John:
It could help except that, respectfully I have to admit, for years I've only 
been putting standpipes in stairs when the level of the highest floor is 30 
feet above the lowest level of fire department access per 905.3.1 and if the 
"AND IN THE LOCATIONS INDICATED IN SECTIONS 905.4, 905.5 and 905.6." applies 
like this, I have to put Class I connections in every stair everywhere 
regardless of building height per 905.4 item 1 except for in an R-3 (905.3 
Exception)

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of John Drucker
Sent: Wednesday, June 03, 2009 3:30 PM
To: [email protected]
Subject: RE: A1 and A2 Standpipes

Mike,

Got it, heres the code path;

"2006 IFC 905.3 Required installations. Standpipe systems shall be
installed where required by Sections 905.3.1 through 905.3.7 AND IN THE
LOCATIONS INDICATED IN SECTIONS 905.4, 905.5 and 905.6. Standpipe
systems are allowed to be combined with automatic sprinkler systems."

The operative code language being; "AND IN THE LOCATIONS INDICATED IN
SECTIONS..... 905.5

905.5.1 Groups A-1 and A-2. In Group A-1 and A-2 occupancies with
occupant loads of more than 1,000, hose connections
shall be located on each side of any stage, on each side of the rear of
the auditorium, on each side of the balcony,and on each tier of dressing
rooms.

The trigger being; "In Group A-1 and A-2 occupancies with OCCUPANT LOADS
OF MORE THAN 1,000"

Also while we are on stages keep the area criteria of 2006 IFC 905.3.4
in mind.

905.3.4 Stages. Stages greater than 1,000 square feet (93m2) in area
shall be equipped with a Class III wet standpipe system with 11/2-inch
and 21/2-inch (38 mm and 64 mm) hose connections on each side of the
stage.
Exception: Where the building or area is equipped throughout with an
automatic sprinkler system, a 11/2 inch (38 mm) hose connection shall be
installed in accordance with NFPA 13 or in accordance with NFPA 14 for
Class II or III standpipes.

Hope that helps,

John Drucker



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Radzicki,
Michael
Sent: Wednesday, June 03, 2009 2:31 PM
To: [email protected]
Subject: RE: A1 and A2 Standpipes

Thank you John: The stage requirements are clear. It's the rear of
auditoriums, balconies, and dressing rooms that appear to have no
requirement but do have a location under 905.5.1. Would a code official
require hose connections in the rear of, say, a school auditorium in
addition to the standpipe connections on either side of the stage in the
front of the auditorium based on this item in IBC, IFC?

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of John
Drucker
Sent: Wednesday, June 03, 2009 2:26 PM
To: [email protected]
Subject: RE: A1 and A2 Standpipes

Hi Mike,

Heres what your looking for;

2006 IBC 410.7 Stages
2006 IFC 914.6 Stages

Hope that helps,

Sincerely

John Drucker
Fire Protection Subcode Official
Fire/Building/Electrical Inspector
New Jersey


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Radzicki,
Michael
Sent: Wednesday, June 03, 2009 1:40 PM
To: [email protected]
Subject: A1 and A2 Standpipes

What is the intent of IFC 2006 item 905.5.1 calling out a location for
Class II hose connections in the rear of auditoriums, balconies, and
dressing rooms of A1 and A2 occupancies when there is no requirement for
Class II systems in these occupancies in neither 905.3 nor the special
detailed requirements of IBC chapter 4?

This e-mail message and any attachments are intended only for the named
recipient(s) above. It may contain confidential information due to its
nature as trade secret, security sensitive, pursuant to contract or
other regards. If you are not the intended recipient, you are hereby
notified that any dissemination or copying of this e-mail and/or any
attachment(s) is strictly prohibited. If you have received this e-mail
in error, please immediately notify the sender by replying to this
e-mail and delete the message and any attachment(s) from your system.

Email transmission cannot be guaranteed to be secure or error-free, as
information could be intercepted, corrupted, lost, destroyed, arrive
late or incomplete, or contain viruses. The recipient should check this
email and any attachments for the presence of viruses. GPI accepts no
liability for any damage caused by errors, omissions or delays arising
from the transmission process or any virus contained in this email.
Please note that any views or opinions presented in this email are
solely those of the author and do not necessarily represent those of GPI
and/or any of its affiliates.
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or
entity to which it is addressed and may contain information that is
privileged and confidential, nor is it, unless specifically stated,
intended to be relied upon by any person or persons other than the
individual or entity named above and no warranties or representations
are made or intended to persons or entities not named above.  If the
reader is not the intended recipient, you are hereby notified that any
dissemination, distribution or copying of this communication is strictly
prohibited.  If you have received this communication in error, please
notify us immediately by telephone, return this message to the address
above and delete all copies.  Thank you.

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

This e-mail message and any attachments are intended only for the named
recipient(s) above. It may contain confidential information due to its
nature as trade secret, security sensitive, pursuant to contract or
other regards. If you are not the intended recipient, you are hereby
notified that any dissemination or copying of this e-mail and/or any
attachment(s) is strictly prohibited. If you have received this e-mail
in error, please immediately notify the sender by replying to this
e-mail and delete the message and any attachment(s) from your system.

Email transmission cannot be guaranteed to be secure or error-free, as
information could be intercepted, corrupted, lost, destroyed, arrive
late or incomplete, or contain viruses. The recipient should check this
email and any attachments for the presence of viruses. GPI accepts no
liability for any damage caused by errors, omissions or delays arising
from the transmission process or any virus contained in this email.
Please note that any views or opinions presented in this email are
solely those of the author and do not necessarily represent those of GPI
and/or any of its affiliates.
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

This e-mail message and any attachments are intended only for the named 
recipient(s) above. It may contain confidential information due to its nature 
as trade secret, security sensitive, pursuant to contract or other regards. If 
you are not the intended recipient, you are hereby notified that any 
dissemination or copying of this e-mail and/or any attachment(s) is strictly 
prohibited. If you have received this e-mail in error, please immediately 
notify the sender by replying to this e-mail and delete the message and any 
attachment(s) from your system.

Email transmission cannot be guaranteed to be secure or error-free, as 
information could be intercepted, corrupted, lost, destroyed, arrive late or 
incomplete, or contain viruses. The recipient should check this email and any 
attachments for the presence of viruses. GPI accepts no liability for any 
damage caused by errors, omissions or delays arising from the transmission 
process or any virus contained in this email. Please note that any views or 
opinions presented in this email are solely those of the author and do not 
necessarily represent those of GPI and/or any of its affiliates.
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to