John: It could help except that, respectfully I have to admit, for years I've only been putting standpipes in stairs when the level of the highest floor is 30 feet above the lowest level of fire department access per 905.3.1 and if the "AND IN THE LOCATIONS INDICATED IN SECTIONS 905.4, 905.5 and 905.6." applies like this, I have to put Class I connections in every stair everywhere regardless of building height per 905.4 item 1 except for in an R-3 (905.3 Exception)
-----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of John Drucker Sent: Wednesday, June 03, 2009 3:30 PM To: [email protected] Subject: RE: A1 and A2 Standpipes Mike, Got it, heres the code path; "2006 IFC 905.3 Required installations. Standpipe systems shall be installed where required by Sections 905.3.1 through 905.3.7 AND IN THE LOCATIONS INDICATED IN SECTIONS 905.4, 905.5 and 905.6. Standpipe systems are allowed to be combined with automatic sprinkler systems." The operative code language being; "AND IN THE LOCATIONS INDICATED IN SECTIONS..... 905.5 905.5.1 Groups A-1 and A-2. In Group A-1 and A-2 occupancies with occupant loads of more than 1,000, hose connections shall be located on each side of any stage, on each side of the rear of the auditorium, on each side of the balcony,and on each tier of dressing rooms. The trigger being; "In Group A-1 and A-2 occupancies with OCCUPANT LOADS OF MORE THAN 1,000" Also while we are on stages keep the area criteria of 2006 IFC 905.3.4 in mind. 905.3.4 Stages. Stages greater than 1,000 square feet (93m2) in area shall be equipped with a Class III wet standpipe system with 11/2-inch and 21/2-inch (38 mm and 64 mm) hose connections on each side of the stage. Exception: Where the building or area is equipped throughout with an automatic sprinkler system, a 11/2 inch (38 mm) hose connection shall be installed in accordance with NFPA 13 or in accordance with NFPA 14 for Class II or III standpipes. Hope that helps, John Drucker -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Radzicki, Michael Sent: Wednesday, June 03, 2009 2:31 PM To: [email protected] Subject: RE: A1 and A2 Standpipes Thank you John: The stage requirements are clear. It's the rear of auditoriums, balconies, and dressing rooms that appear to have no requirement but do have a location under 905.5.1. Would a code official require hose connections in the rear of, say, a school auditorium in addition to the standpipe connections on either side of the stage in the front of the auditorium based on this item in IBC, IFC? -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of John Drucker Sent: Wednesday, June 03, 2009 2:26 PM To: [email protected] Subject: RE: A1 and A2 Standpipes Hi Mike, Heres what your looking for; 2006 IBC 410.7 Stages 2006 IFC 914.6 Stages Hope that helps, Sincerely John Drucker Fire Protection Subcode Official Fire/Building/Electrical Inspector New Jersey -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Radzicki, Michael Sent: Wednesday, June 03, 2009 1:40 PM To: [email protected] Subject: A1 and A2 Standpipes What is the intent of IFC 2006 item 905.5.1 calling out a location for Class II hose connections in the rear of auditoriums, balconies, and dressing rooms of A1 and A2 occupancies when there is no requirement for Class II systems in these occupancies in neither 905.3 nor the special detailed requirements of IBC chapter 4? This e-mail message and any attachments are intended only for the named recipient(s) above. It may contain confidential information due to its nature as trade secret, security sensitive, pursuant to contract or other regards. If you are not the intended recipient, you are hereby notified that any dissemination or copying of this e-mail and/or any attachment(s) is strictly prohibited. If you have received this e-mail in error, please immediately notify the sender by replying to this e-mail and delete the message and any attachment(s) from your system. Email transmission cannot be guaranteed to be secure or error-free, as information could be intercepted, corrupted, lost, destroyed, arrive late or incomplete, or contain viruses. The recipient should check this email and any attachments for the presence of viruses. GPI accepts no liability for any damage caused by errors, omissions or delays arising from the transmission process or any virus contained in this email. Please note that any views or opinions presented in this email are solely those of the author and do not necessarily represent those of GPI and/or any of its affiliates. _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) CONFIDENTIAL AND PROPRIETARY: This email message is intended only for the use of the individual or entity to which it is addressed and may contain information that is privileged and confidential, nor is it, unless specifically stated, intended to be relied upon by any person or persons other than the individual or entity named above and no warranties or representations are made or intended to persons or entities not named above. If the reader is not the intended recipient, you are hereby notified that any dissemination, distribution or copying of this communication is strictly prohibited. If you have received this communication in error, please notify us immediately by telephone, return this message to the address above and delete all copies. Thank you. _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) This e-mail message and any attachments are intended only for the named recipient(s) above. It may contain confidential information due to its nature as trade secret, security sensitive, pursuant to contract or other regards. If you are not the intended recipient, you are hereby notified that any dissemination or copying of this e-mail and/or any attachment(s) is strictly prohibited. If you have received this e-mail in error, please immediately notify the sender by replying to this e-mail and delete the message and any attachment(s) from your system. Email transmission cannot be guaranteed to be secure or error-free, as information could be intercepted, corrupted, lost, destroyed, arrive late or incomplete, or contain viruses. The recipient should check this email and any attachments for the presence of viruses. GPI accepts no liability for any damage caused by errors, omissions or delays arising from the transmission process or any virus contained in this email. Please note that any views or opinions presented in this email are solely those of the author and do not necessarily represent those of GPI and/or any of its affiliates. _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) This e-mail message and any attachments are intended only for the named recipient(s) above. It may contain confidential information due to its nature as trade secret, security sensitive, pursuant to contract or other regards. If you are not the intended recipient, you are hereby notified that any dissemination or copying of this e-mail and/or any attachment(s) is strictly prohibited. If you have received this e-mail in error, please immediately notify the sender by replying to this e-mail and delete the message and any attachment(s) from your system. Email transmission cannot be guaranteed to be secure or error-free, as information could be intercepted, corrupted, lost, destroyed, arrive late or incomplete, or contain viruses. The recipient should check this email and any attachments for the presence of viruses. GPI accepts no liability for any damage caused by errors, omissions or delays arising from the transmission process or any virus contained in this email. Please note that any views or opinions presented in this email are solely those of the author and do not necessarily represent those of GPI and/or any of its affiliates. _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)