A Class II standpipe is required for those conditions set forth in
Section 905.5. It seems odd that one can eliminate the Class I standpipe
when the building is protected in accordance with NFPA 13 yet the design
professional is required to provide the Class II standpipe, and it is.
This is an old provision that came out of the AIA (American Insurance
Association) building code in response to the Iroquois Theater fire.
It's a provision that should be deleted but no one has ever submitted a
code change to do this, so you're stuck with the requirement unless you
develop a reasonable alternative materials and method for approval by
the code official. 


Scott Stookey
Senior Technical Staff - Business & Product Development
International Code Council (ICC)
807 Sweetwater River Drive
Austin, Texas 78748-2238
Office: 1-888-422-7233 (ICC-SAFE) X 3473 (FIRE)
Cellular: 512-716-9595
[email protected]
www.iccsafe.org
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Radzicki,
Michael
Sent: Wednesday, June 03, 2009 12:40 PM
To: [email protected]
Subject: A1 and A2 Standpipes

What is the intent of IFC 2006 item 905.5.1 calling out a location for
Class II hose connections in the rear of auditoriums, balconies, and
dressing rooms of A1 and A2 occupancies when there is no requirement for
Class II systems in these occupancies in neither 905.3 nor the special
detailed requirements of IBC chapter 4?

This e-mail message and any attachments are intended only for the named
recipient(s) above. It may contain confidential information due to its
nature as trade secret, security sensitive, pursuant to contract or
other regards. If you are not the intended recipient, you are hereby
notified that any dissemination or copying of this e-mail and/or any
attachment(s) is strictly prohibited. If you have received this e-mail
in error, please immediately notify the sender by replying to this
e-mail and delete the message and any attachment(s) from your system.

Email transmission cannot be guaranteed to be secure or error-free, as
information could be intercepted, corrupted, lost, destroyed, arrive
late or incomplete, or contain viruses. The recipient should check this
email and any attachments for the presence of viruses. GPI accepts no
liability for any damage caused by errors, omissions or delays arising
from the transmission process or any virus contained in this email.
Please note that any views or opinions presented in this email are
solely those of the author and do not necessarily represent those of GPI
and/or any of its affiliates.
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to