Yes based on ... ???    There is no special systems requirement in
Chapter 4 for the A-1 or A-2, so I would look to the code for guidance
as to when they are required.   As best as we can find, there is no
requirement for a Class II in the back of house, for stages over 1,000
s.f.   If there was a Class III triggered, we could eliminate the Class
II hose stations per NFPA 14 (sprinklers throughout), but that's not the
case here.   While I hear you loud and clear about the intent being to
apply 9.5.1 as a prescriptive requirement for those hose stations,
that's not how the rest of the article is written or applied, IMHO.

Steve Leyton
Protection Design & Consulting
San Diego, CA




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Scott
Stookey
Sent: Wednesday, June 03, 2009 11:33 AM
To: [email protected]
Subject: RE: A1 and A2 Standpipes

Yes

Scott Stookey
Senior Technical Staff - Business & Product Development
International Code Council (ICC)
807 Sweetwater River Drive
Austin, Texas 78748-2238
Office: 1-888-422-7233 (ICC-SAFE) X 3473 (FIRE)
Cellular: 512-716-9595
[email protected]
www.iccsafe.org
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Radzicki,
Michael
Sent: Wednesday, June 03, 2009 1:31 PM
To: [email protected]
Subject: RE: A1 and A2 Standpipes

Thank you John: The stage requirements are clear. It's the rear of
auditoriums, balconies, and dressing rooms that appear to have no
requirement but do have a location under 905.5.1. Would a code official
require hose connections in the rear of, say, a school auditorium in
addition to the standpipe connections on either side of the stage in the
front of the auditorium based on this item in IBC, IFC?

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of John
Drucker
Sent: Wednesday, June 03, 2009 2:26 PM
To: [email protected]
Subject: RE: A1 and A2 Standpipes

Hi Mike,

Heres what your looking for;

2006 IBC 410.7 Stages
2006 IFC 914.6 Stages

Hope that helps,

Sincerely

John Drucker
Fire Protection Subcode Official
Fire/Building/Electrical Inspector
New Jersey


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Radzicki,
Michael
Sent: Wednesday, June 03, 2009 1:40 PM
To: [email protected]
Subject: A1 and A2 Standpipes

What is the intent of IFC 2006 item 905.5.1 calling out a location for
Class II hose connections in the rear of auditoriums, balconies, and
dressing rooms of A1 and A2 occupancies when there is no requirement for
Class II systems in these occupancies in neither 905.3 nor the special
detailed requirements of IBC chapter 4?

This e-mail message and any attachments are intended only for the named
recipient(s) above. It may contain confidential information due to its
nature as trade secret, security sensitive, pursuant to contract or
other regards. If you are not the intended recipient, you are hereby
notified that any dissemination or copying of this e-mail and/or any
attachment(s) is strictly prohibited. If you have received this e-mail
in error, please immediately notify the sender by replying to this
e-mail and delete the message and any attachment(s) from your system.

Email transmission cannot be guaranteed to be secure or error-free, as
information could be intercepted, corrupted, lost, destroyed, arrive
late or incomplete, or contain viruses. The recipient should check this
email and any attachments for the presence of viruses. GPI accepts no
liability for any damage caused by errors, omissions or delays arising
from the transmission process or any virus contained in this email.
Please note that any views or opinions presented in this email are
solely those of the author and do not necessarily represent those of GPI
and/or any of its affiliates.
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or
entity to which it is addressed and may contain information that is
privileged and confidential, nor is it, unless specifically stated,
intended to be relied upon by any person or persons other than the
individual or entity named above and no warranties or representations
are made or intended to persons or entities not named above.  If the
reader is not the intended recipient, you are hereby notified that any
dissemination, distribution or copying of this communication is strictly
prohibited.  If you have received this communication in error, please
notify us immediately by telephone, return this message to the address
above and delete all copies.  Thank you.

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

This e-mail message and any attachments are intended only for the named
recipient(s) above. It may contain confidential information due to its
nature as trade secret, security sensitive, pursuant to contract or
other regards. If you are not the intended recipient, you are hereby
notified that any dissemination or copying of this e-mail and/or any
attachment(s) is strictly prohibited. If you have received this e-mail
in error, please immediately notify the sender by replying to this
e-mail and delete the message and any attachment(s) from your system.

Email transmission cannot be guaranteed to be secure or error-free, as
information could be intercepted, corrupted, lost, destroyed, arrive
late or incomplete, or contain viruses. The recipient should check this
email and any attachments for the presence of viruses. GPI accepts no
liability for any damage caused by errors, omissions or delays arising
from the transmission process or any virus contained in this email.
Please note that any views or opinions presented in this email are
solely those of the author and do not necessarily represent those of GPI
and/or any of its affiliates.
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 4128 (20090603) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to