Yes based on ... ??? There is no special systems requirement in Chapter 4 for the A-1 or A-2, so I would look to the code for guidance as to when they are required. As best as we can find, there is no requirement for a Class II in the back of house, for stages over 1,000 s.f. If there was a Class III triggered, we could eliminate the Class II hose stations per NFPA 14 (sprinklers throughout), but that's not the case here. While I hear you loud and clear about the intent being to apply 9.5.1 as a prescriptive requirement for those hose stations, that's not how the rest of the article is written or applied, IMHO.
Steve Leyton Protection Design & Consulting San Diego, CA -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Scott Stookey Sent: Wednesday, June 03, 2009 11:33 AM To: [email protected] Subject: RE: A1 and A2 Standpipes Yes Scott Stookey Senior Technical Staff - Business & Product Development International Code Council (ICC) 807 Sweetwater River Drive Austin, Texas 78748-2238 Office: 1-888-422-7233 (ICC-SAFE) X 3473 (FIRE) Cellular: 512-716-9595 [email protected] www.iccsafe.org -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Radzicki, Michael Sent: Wednesday, June 03, 2009 1:31 PM To: [email protected] Subject: RE: A1 and A2 Standpipes Thank you John: The stage requirements are clear. It's the rear of auditoriums, balconies, and dressing rooms that appear to have no requirement but do have a location under 905.5.1. Would a code official require hose connections in the rear of, say, a school auditorium in addition to the standpipe connections on either side of the stage in the front of the auditorium based on this item in IBC, IFC? -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of John Drucker Sent: Wednesday, June 03, 2009 2:26 PM To: [email protected] Subject: RE: A1 and A2 Standpipes Hi Mike, Heres what your looking for; 2006 IBC 410.7 Stages 2006 IFC 914.6 Stages Hope that helps, Sincerely John Drucker Fire Protection Subcode Official Fire/Building/Electrical Inspector New Jersey -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Radzicki, Michael Sent: Wednesday, June 03, 2009 1:40 PM To: [email protected] Subject: A1 and A2 Standpipes What is the intent of IFC 2006 item 905.5.1 calling out a location for Class II hose connections in the rear of auditoriums, balconies, and dressing rooms of A1 and A2 occupancies when there is no requirement for Class II systems in these occupancies in neither 905.3 nor the special detailed requirements of IBC chapter 4? This e-mail message and any attachments are intended only for the named recipient(s) above. It may contain confidential information due to its nature as trade secret, security sensitive, pursuant to contract or other regards. If you are not the intended recipient, you are hereby notified that any dissemination or copying of this e-mail and/or any attachment(s) is strictly prohibited. If you have received this e-mail in error, please immediately notify the sender by replying to this e-mail and delete the message and any attachment(s) from your system. Email transmission cannot be guaranteed to be secure or error-free, as information could be intercepted, corrupted, lost, destroyed, arrive late or incomplete, or contain viruses. The recipient should check this email and any attachments for the presence of viruses. GPI accepts no liability for any damage caused by errors, omissions or delays arising from the transmission process or any virus contained in this email. Please note that any views or opinions presented in this email are solely those of the author and do not necessarily represent those of GPI and/or any of its affiliates. _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) CONFIDENTIAL AND PROPRIETARY: This email message is intended only for the use of the individual or entity to which it is addressed and may contain information that is privileged and confidential, nor is it, unless specifically stated, intended to be relied upon by any person or persons other than the individual or entity named above and no warranties or representations are made or intended to persons or entities not named above. If the reader is not the intended recipient, you are hereby notified that any dissemination, distribution or copying of this communication is strictly prohibited. If you have received this communication in error, please notify us immediately by telephone, return this message to the address above and delete all copies. Thank you. _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) This e-mail message and any attachments are intended only for the named recipient(s) above. It may contain confidential information due to its nature as trade secret, security sensitive, pursuant to contract or other regards. If you are not the intended recipient, you are hereby notified that any dissemination or copying of this e-mail and/or any attachment(s) is strictly prohibited. If you have received this e-mail in error, please immediately notify the sender by replying to this e-mail and delete the message and any attachment(s) from your system. Email transmission cannot be guaranteed to be secure or error-free, as information could be intercepted, corrupted, lost, destroyed, arrive late or incomplete, or contain viruses. The recipient should check this email and any attachments for the presence of viruses. GPI accepts no liability for any damage caused by errors, omissions or delays arising from the transmission process or any virus contained in this email. Please note that any views or opinions presented in this email are solely those of the author and do not necessarily represent those of GPI and/or any of its affiliates. _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) __________ Information from ESET NOD32 Antivirus, version of virus signature database 4128 (20090603) __________ The message was checked by ESET NOD32 Antivirus. http://www.eset.com _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)