Did you make the pumper modifications that are req'd per NFPA 291.  For
pitot less than 7 on a pumper outlet, you are supposed to use the same
formula for the 2.5" outlet, then multiple the flow by 0.83, if I recall
correctly.  Just check 291 for the exact values.

In theory, you are drawing a straight line and it should model out close,
within error of gauges and humans reading the gauges.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Richard
Lindner
Sent: Tuesday, June 23, 2009 12:25 PM
To: sprinklerforum
Subject: Hydrant Flow test results

Have a question regarding hydrant flow tests.

We have received a report where the contractor flow a single 2 1/2" outlet
and gave us static, residual, pitot and calculated flow.  He then performed
another test using the 4 1/2" outlet on the hydrant, again giving us values.

Plotting the graph, is there supposed to be a correlation between the
testing of the 2 1/2" versus the 4 1/2" or are they supposed to be used
separately.  For example, when graphing the 2 1/2" outlet, the 4 1/2" outlet
info should be hitting this line or not??

Also, is a pitot reading of a range of 4 to say 8 on a 4 1/2" outlet valid
data?

We're not sure how to use this info.

Richard
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

__________ NOD32 4181 (20090623) Information __________

This message was checked by NOD32 antivirus system.
http://www.eset.com


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to