Ok, I'll bite.
When you say two-hydrant flow test, you are talking about static and
residual erad at hydrant A, and flow from hydrant B?

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bobby
McCullough
Sent: Tuesday, June 23, 2009 4:35 PM
To: [email protected]
Subject: RE: Hydrant Flow test results

Have a look at AWWA Manual M17 - Installation, Field Testing, and
Maintenance of Fire Hydrants.  A couple municipalities in the metro area
require all flow tests comply with M17; whether it be a flow test for
hydraulic calculations or testing a hydrant as required by NFPA 25.  I
believe M17 only addresses two hydrant tests, never a single.

Bobby McCullough
Atlanta Sprinkler Inspection
[email protected] 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Paul
Pinigis
Sent: Tuesday, June 23, 2009 3:33 PM
To: [email protected]
Subject: RE: Hydrant Flow test results

Any single-hydrant test is questionable to begin with, but if two tests
are done they should yield identical graphs.  Pitot pressures of less
than 10 psi are generally unacceptable.  

Paul Pinigis, P.E.
Life Safety Department Head




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Richard
Lindner
Sent: Tuesday, June 23, 2009 3:25 PM
To: sprinklerforum
Subject: Hydrant Flow test results

Have a question regarding hydrant flow tests.

We have received a report where the contractor flow a single 2 1/2"
outlet
and gave us static, residual, pitot and calculated flow.  He then
performed
another test using the 4 1/2" outlet on the hydrant, again giving us
values.

Plotting the graph, is there supposed to be a correlation between the
testing of the 2 1/2" versus the 4 1/2" or are they supposed to be used
separately.  For example, when graphing the 2 1/2" outlet, the 4 1/2"
outlet
info should be hitting this line or not??

Also, is a pitot reading of a range of 4 to say 8 on a 4 1/2" outlet
valid
data?

We're not sure how to use this info.

Richard
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to