I have a picture of a hollow stream.  It is from a 3/4" pipe (the inspectors
test, without an orifice), and shows a piece of trash stationary in the
stream.  On examination afterward, the trash seemed to be the remains of a
cocoon.  I can send the pic to anyone interested.

Ed

On Tue, Jun 23, 2009 at 1:52 PM, Ed Kramer <[email protected]> wrote:

> In theory, the two flow graphs should be identical.  In reality, they
> should
> be reasonably similar.  As others have pointed out, the source of the water
> (purely gravity vs gravity w/pumps) and pressure reducing devices can
> really
> confuse things.
>
> A few observations:  a) Unless the flow is very high, pitot readings from a
> 4.5" outlet can be very wrong.  On several occasions, I've seen hollow
> (literally) streams coming from the 4.5".  When the pitot was placed in the
> center of the outlet, the reading was zero.  To get a reading, had to move
> the pitot toward an edge.  Got a reading, but it grossly overestimated the
> actual flow.  b) If the 2.5' outlet flowed anything close to the combined
> sprinkler/hose demand, use those numbers.  c) I wouldn't trust any pitot
> reading less than 10.  If necessary, connect a smaller orifice to the
> outlet
> - the flow will be less but the pitot reading will be greater.  d) a
> single-hydrant flow test is not recommended procedure, but if it can't be
> avoided, the results tend to be conservative.
>
> Curious - what are the exact numbers you're working with?
>
> Ed Kramer
> Littleton, CO
>

-- 
Ed Vining
4819 John Muir Rd
Martinez CA 94553
925-228-8792
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to