FM 7-88 was the data sheet on Storage Tanks for Flammable and Combustible
Liquids.  The latest revision date on the paper copy I have is May 1999.
I don't think it would have applied in your case.  The guideline for indoor
storage tanks of one or more tanks is a maximum of 10,000 gallons if the
liquid is a class 1 liquid.  You are way over that.  And of course they
require sprinklers and drainage to a safe location for the tank spill and
sprinkler discharge water.  I am guessing it was their version of NFPA 30.

John Hoffman P.E. | Fire Protection Engineer | Facility Engineering
Services, KCP, LLC - Burns & McDonnell Engineering | National Nuclear
Security Administration's Kansas City Plant | Operated by Honeywell FM&T |
2000 E. 95th St | Kansas City, MO  64131 | ph 816-997-7213


                                                                                
                                       
  From:       "Chris Cahill" <[email protected]>                          
                                       
                                                                                
                                       
  To:         <[email protected]>                                
                                       
                                                                                
                                       
  Date:       07/06/2009 03:47 PM                                               
                                       
                                                                                
                                       
  Subject:    Class IB & IC Water Miscible                                      
                                       
                                                                                
                                       
  Sent by:    [email protected]                          
                                       
                                                                                
                                       





Class IB & IC Water Miscible - Think liquor



Stationary tanks - 15,000 gallons each, 18 within containment area inside a
building.  Think one hell of a party.



Got a code reference to a sprinkler density/protection scheme?  FM 7-29
references a 7-88 but I can't find any 7-88.  NFPA 30 (24.6) doesn't seem
to
say anything much about this even suggesting it's OK with none (after a
hazard analysis, of course).  If the goal is to keep a fire not involving
the liquid from breaking a tank probably don't need much density.  If the
goal is to save anything after a tank rupture and fire then foam is
probably
the only answer.  I'd think the code or standard would say something?
Most
of the building is drums in racks so I think were at .6/3000 plus in-racks.
Thinking just extending into this small area has very little cost.



Yes, yes I know PE should be involved to specify the approach for the
holistic fire protection matters including spill containment, venting, tank
specifications, electrical concerns etc.  Lets for now assume this is the
real ugly world and this party doesn't exist yet.



Chris Cahill, P.E.

Fire Protection Engineer

Sentry Fire Protection, Inc.



763-658-4483

763-658-4921 fax



Email: [email protected]



Mail: P.O. Box 69

        Waverly, MN 55390



Location: 4439 Hwy 12 SW

              Waverly, MN 55390



_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)



_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to