Where is the 10,000 gallon limit referenced?

 


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of [email protected]
Sent: Monday, July 06, 2009 5:07 PM
To: [email protected]
Subject: Re: Class IB & IC Water Miscible

FM 7-88 was the data sheet on Storage Tanks for Flammable and Combustible 
Liquids.  The latest revision date on the paper copy I have is May 1999.
I don't think it would have applied in your case.  The guideline for indoor 
storage tanks of one or more tanks is a maximum of 10,000 gallons if the liquid 
is a class 1 liquid.  You are way over that.  And of course they require 
sprinklers and drainage to a safe location for the tank spill and sprinkler 
discharge water.  I am guessing it was their version of NFPA 30.

John Hoffman P.E. | Fire Protection Engineer | Facility Engineering Services, 
KCP, LLC - Burns & McDonnell Engineering | National Nuclear Security 
Administration's Kansas City Plant | Operated by Honeywell FM&T | 2000 E. 95th 
St | Kansas City, MO  64131 | ph 816-997-7213


                                                                                
                                       
  From:       "Chris Cahill" <[email protected]>                          
                                       
                                                                                
                                       
  To:         <[email protected]>                                
                                       
                                                                                
                                       
  Date:       07/06/2009 03:47 PM                                               
                                       
                                                                                
                                       
  Subject:    Class IB & IC Water Miscible                                      
                                       
                                                                                
                                       
  Sent by:    [email protected]                          
                                       
                                                                                
                                       





Class IB & IC Water Miscible - Think liquor



Stationary tanks - 15,000 gallons each, 18 within containment area inside a 
building.  Think one hell of a party.



Got a code reference to a sprinkler density/protection scheme?  FM 7-29 
references a 7-88 but I can't find any 7-88.  NFPA 30 (24.6) doesn't seem to 
say anything much about this even suggesting it's OK with none (after a hazard 
analysis, of course).  If the goal is to keep a fire not involving the liquid 
from breaking a tank probably don't need much density.  If the goal is to save 
anything after a tank rupture and fire then foam is probably the only answer.  
I'd think the code or standard would say something?
Most
of the building is drums in racks so I think were at .6/3000 plus in-racks.
Thinking just extending into this small area has very little cost.



Yes, yes I know PE should be involved to specify the approach for the holistic 
fire protection matters including spill containment, venting, tank 
specifications, electrical concerns etc.  Lets for now assume this is the real 
ugly world and this party doesn't exist yet.



Chris Cahill, P.E.

Fire Protection Engineer

Sentry Fire Protection, Inc.



763-658-4483

763-658-4921 fax



Email: [email protected]



Mail: P.O. Box 69

        Waverly, MN 55390



Location: 4439 Hwy 12 SW

              Waverly, MN 55390



_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)



_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to