Hello Jay,

Yes there is NFPA 13 2007 edition

6.1.2.2 Reconditioned sprinklers shall not be permitted to be utilized on
any new or existing system.

6.2.1 General. Only new sprinklers shall be installed.

Wednesday, July 8, 2009, 7:48:33 PM, you wrote:

> Is there some where written that says you cant reinstall the heads after
> removal?  I am coming up blank in my search on this old rule.  

> JB


>       