Hello Jay, Yes there is NFPA 13 2007 edition
6.1.2.2 Reconditioned sprinklers shall not be permitted to be utilized on any new or existing system. 6.2.1 General. Only new sprinklers shall be installed. Wednesday, July 8, 2009, 7:48:33 PM, you wrote: > Is there some where written that says you cant reinstall the heads after > removal? I am coming up blank in my search on this old rule. > JB > > _______________________________________________ > Sprinklerforum mailing list > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > For Technical Assistance, send an email to: [email protected] > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) -- Best regards, Charles Thurston mailto:[email protected] Coastal Fire Protection _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)