What kind of a liability issue are you creating by messing around 
with a compressor that says not to mess around with it? You may need 
to think new compressor.


At 08:20 AM 7/9/2009, you wrote:
>Good morning Campers,
>
>I have a dry pipe valve to replace and the client has expressed interest in
>a low differential replacement.
>The system is 25 years old and has a slow leak "somewhere" that we've not
>been able to locate, even after flooding.
>The air compressor is just a riser mount and with this new valve, air
>pressure will drop from 45 to +/-20, 110 PSI water.
>The pressure switch on the compressor has labels stating not to adjust it
>and leave it factory set, 35-45 PSI.
>I don't think I can put a regulating assembly on a riser mount, saw one once
>and it telegraphed badly between the compressor and regulator.  I could
>change the pressure switch to a lower rated line switch.  I could also
>install a regulating assembly with switch and re-wire the compressor to the
>new switch.  What would you guys suggest?
>
>Tom Duross
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to