Were/are there any leaks in the dry valve or trim?

At 11:39 AM 7/9/2009, you wrote:
>Very little grooved, just repairs made in the last 10+ years.  It's all
>Sch40 threaded, 1"-4", threaded flanges.  This is just our 3rd year here,
>last year when we did a full flood we attached a pump and took it to 200
>looking for leaks but couldn't find anything.  I'm thinking the leak is
>concealed behind old plaster walls.  It does an unheated attic, traditional
>piping arrangement.  I'm guessing 40 years old with a 15 year old dry valve
>and compressor.  I'm told the compressor runs about once a day for a few
>minutes.  They lost power last Friday and the valve tripped about 4 AM on
>the 4th, I spent most of the morning chasing low points and resetting it.
>The compressor was tripped out so I'm thinking it went out on overload from
>running so long, I did mention it shouldn't and suggested rewiring it to the
>generator.  It's a long term care facility right near NFPA in Quincy.  I'm
>aware of the allowable leakage but sometimes (like this) have a hard time
>applying it.  I did consider a scent test but if we couldn't even find a
>drip at 200, would this help?
>I'm getting splinters scratching my head but I have tweezers.
>TD
>
>
>
>We have done this a couple times and have always replaced the compressor.
>However, a word of warning inspired by learning the hard way. Assuming this
>is a grooved system, when you drop the pressure the entire thing can start
>leaking like a sieve.  Older couplings can be a little brittle and less
>resilient.  They just don't like to seal correctly under the lower pressure.
>
>Best of luck!
>
>Lori Kitchen
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to