There is some info in NFPA 15 concerning sizes of pipe used for stands and 
height limitations.

NFPA 15-2007, 6.3.2.2.1.

Anvil has some pipe stanchions and saddles.  There are probably others as well. 
 Or make your own.

I doubt you're going to find one that's actually "listed".


http://www.anvilintl.com/ProductSearch/ProductInfo.aspx?productId=9611 


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Tuesday, August 04, 2009 4:25 PM
To: [email protected]
Subject: pipe stands

NFPA 13 (2007) section 9.2.6.2 says that if pipe stands are used, they must be 
approved.

1. Are there any approved pipe stands?
2. Outside of the general comment on support of pipe, is there anything 
specific on pipe stands in 2002? I couldn't find anything.
3. When calculating the weight of water-filled pipe for a riser manifold, am I 
correct in assuming that the equipment and the vertical piping would need to be 
considered? Has anyone actually done this?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to