TOLCO has stands from Fig. 311 to 319 some of which are MSS-SP-69 which I
believe that NFPA 13 refers to "Listed" "In a published list" and as
acceptable to the AHJ. I would say that MSS-SP-69 meets that definition.
(Military jobs often require the MSS approved hangers) 

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Tuesday, August 04, 2009 2:30 PM
To: [email protected]
Subject: Re: pipe stands

Approved means acceptable to the AHJ.  Not listed.
John
Sent from my BlackBerryR smartphone with Nextel Direct Connect

-----Original Message-----
From: [email protected]

Date: Tue, 04 Aug 2009 16:27:54 
To: <[email protected]>
Subject: Re: pipe stands


I think Tyco sells approved stands


-----Original Message-----
From: Todd Williams <[email protected]>
To: [email protected]
Sent: Tue, Aug 4, 2009 4:25 pm
Subject: pipe stands



NFPA 13 (2007) section 9.2.6.2 says that if pipe stands are used, 
they must be approved.

1. Are there any approved pipe stands?
2. Outside of the general comment on support of pipe, is there 
anything specific on pipe stands in 2002? I couldn't find anything.
3. When calculating the weight of water-filled pipe for a riser 
manifold, am I correct in assuming that the equipment and the 
vertical piping would need to be considered? Has anyone actually done this?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080 
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to