Ralphy, Would I be correct in assuming that you're looking at a pressure reducing valve because of a variable pressure water supply? If so, I have used Cla-Val 90G-21.
Also, I believe there are some diesel engines now with governors that will automatically adjust, but I am not up on the details. Regards, James L.(Jim) Roberts, PE/SET Fluor Corporation 100 Fluor Daniel Drive - C104F Greenville, SC 29607 864.281.5149 864.281.4916(Fax) Ralphy Henderson <[email protected]> Sent by: [email protected] 08/04/2009 05:35 PM Please respond to sprinklerforum To [email protected] cc Subject Diesel Fire Pump with Pressure Reducing Valve Would anyone happen to have an example of a diesel driven fire pump with a pressure reducing valve downstream? I'm tossing around the options with our estimators and we'd like to compare pump room sizes etc...with projects that we've already done consisting of electric driven pumps (which we mostly do). Thanks,Ralphy _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) ------------------------------------------------------------ The information transmitted is intended only for the person or entity to which it is addressed and may contain proprietary, business-confidential and/or privileged material. If you are not the intended recipient of this message you are hereby notified that any use, review, retransmission, dissemination, distribution, reproduction or any action taken in reliance upon this message is prohibited. If you received this in error, please contact the sender and delete the material from any computer. Any views expressed in this message are those of the individual sender and may not necessarily reflect the views of the company. ------------------------------------------------------------ _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)