Can you use a lower-rated pump and still make the calc's work with larger pipe 
sizes or different (larger) ESFR K-factor?  It's not a good practice to 
arbitrarily over design a pump and then use a device ramp the discharge 
pressure back down, especially if the only reason is to save on pipe sizing.   
How much differential is there between highest anticipated churn and minimum 
required residual?   Also, what are the required flow and pump rating in GPMv




  
Sent from my Verizon Wireless BlackBerry

-----Original Message-----
From: Ralphy Henderson <[email protected]>

Date: Wed, 5 Aug 2009 07:27:03 
To: <[email protected]>
Subject: RE: Diesel Fire Pump with Pressure Reducing Valve


Sure, this is for ESFR drawing off city water supply. We're looking at 
potentially high pressures at churn and operation of first few sprinklers. 

--- On Tue, 8/4/09, Steve Leyton <[email protected]> wrote:

From: Steve Leyton <[email protected]>
Subject: RE: Diesel Fire Pump with Pressure Reducing Valve
To: [email protected]
Date: Tuesday, August 4, 2009, 9:57 PM

If I might ask, what is the application?  In other words, why the reducing 
valve and how is the discharge main to be configured?

Steve Leyton
Protection Design & Consulting
San Diego, CA




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Ralphy Henderson
Sent: Tuesday, August 04, 2009 2:36 PM
To: [email protected]
Subject: Diesel Fire Pump with Pressure Reducing Valve

Would anyone happen to have an example of a diesel driven fire pump with a 
pressure reducing valve downstream? I'm tossing around the options with our 
estimators and we'd like to compare pump room sizes etc...with projects that 
we've already done consisting of electric driven pumps (which we mostly 
do). Thanks,Ralphy


      
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
 

__________ Information from ESET NOD32 Antivirus, version of virus signature 
database 4306 (20090804)__________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
 

__________ Information from ESET NOD32 Antivirus, version of virus signature 
database 4306 (20090804)__________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)



      
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to