You're asking an open ended question.  Sorry for running you around in circles.

There are too many unknown variables here that are needed to make any kind of 
determination.

Like has been said, how much pipe, fittings, valves, elevations, what kind of 
discharge gpm, etc. etc, etc.

Plus the value at what tank level, since the tank head will affect the residual 
pressure.  

If you go by the flow required to produce a 10 fps velocity out of NFPA 24 for 
instance, that flow rate for an 8" would be 1560 gpm.

If you use cement lined DI pipe at 1560 gpm the pressure drop is .156 psi/10ft.

Ina real simplistic format, if you had 20 ft of pipe, static of 70 psi, flowing 
1560 gpm, the line loss equals .313 psi.  Use 1560 gpm and 69.6 psi for the 
K-factor which comes out to K=197.8.   Naturally the gpm will be slightly less 
than at the discharge but that difference would be negligible at these 
variables. 

This is all nominal since like I said the value will vary depending on tank 
level and other unknowns.  



Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Greg McGahan
Sent: Thursday, August 06, 2009 9:37 AM
To: [email protected]
Subject: RE: water storage tank

Guys, I know all of the basic hydraulic stuff....I do NOT know the K factor of 
an 8" open pipe and don't feel comfortable guessing at formulas. I went to 
college and I know there is a formula that will easily tell you a reasonable 
expected flow and pressure. Bu that was a long time ago.

Greg McGahan
Operations Manager

Living Water Fire Protection
1160 McKenzie Road
P.O. Box 877
Cantonment, Florida 32533
(850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231 [email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Thursday, August 06, 2009 8:29 AM
To: AFSA
Subject: Re: water storage tank

That depends on flow rate Greg. Higher flow = higher loss per ft.  Longer run = 
higher loss at specified flow rate.  




Sent from my Verizon Wireless BlackBerry

-----Original Message-----
From: "Greg McGahan" <[email protected]>

Date: Thu, 6 Aug 2009 08:06:45
To: <[email protected]>
Subject: RE: water storage tank


I know the static pressure. I need the RESIDUAL pressure and flow through an 
open 8" pipe at ground level.

Greg McGahan
Operations Manager

Living Water Fire Protection
1160 McKenzie Road
P.O. Box 877
Cantonment, Florida 32533
(850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Thursday, August 06, 2009 7:28 AM
To: [email protected]
Subject: RE: water storage tank

The formula is: ft of water x .433 = psi

So for 140 ft of head the approximate psi would be around 60 psi, at 70 ft it 
would be approximately 30, etc.

Note that this does not account for the loss through the tank outlet, vortex 
plate valves or piping loss.   

Find out what that 8" is.  Especially if it's a plastic.  Beware of HDPE.


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Greg McGahan
Sent: Thursday, August 06, 2009 8:18 AM
To: [email protected]
Subject: water storage tank

We have a situation where a new water storage tank is being installed on a 
public utility system and I need some help if anyone can tell me the following:

New Tank - 140' high

8" pipe (unknown type) going straight to ground level

What is a reasonable expected flow and residual pressure?

Any help would be appreciated.

Greg McGahan
Operations Manager

Living Water Fire Protection
1160 McKenzie Road
P.O. Box 877
Cantonment, Florida 32533
(850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231 [email protected]


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to