FWIW:

I was digging through some old project data where we had some flow information 
from a similar arrangement.

The 250,000 gallon elevated tank, B.O.T. was 140ft, with a 10" riser serving a 
10" underground fire main.  Residual flow at the hydrant nearest the tank 
revealed approximately 2100 gpm at 65 psi.

Loss through the 10" riser using HW would indicate about a 1.7 psi loss for the 
140 ft.

And BTW, the risers are usually steel not DI.  So different C-factor, makes a 
little difference in the loss. 

Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Mark Sornsin
Sent: Thursday, August 06, 2009 3:36 PM
To: '[email protected]'
Subject: RE: water storage tank

The correct calculation is 0.156 x 14 not 140 (the formula given earlier was 
0.156 psi/10 ft.).

So your loss through 140 ft. of cement lined ductile iron would be 2.2 psi at 
1,560 gpm.

[that loss per foot of DI pipe seems a little high to me, but its prolly good 
enough for these purposes]

Mark A. Sornsin, PE
Fire Protection Engineer
Ulteig Engineers, Inc.
Fargo, ND
Direct:    701. 280.8591
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Greg McGahan
Sent: Thursday, August 06, 2009 1:37 PM
To: [email protected]
Subject: RE: water storage tank

You are correct....the answer I got was "we don't know"........from the horse's 
mouth. Thanks for all of your help, I will let you know how it works out in a 
few hours.

Greg McGahan
Operations Manager

Living Water Fire Protection
1160 McKenzie Road
P.O. Box 877
Cantonment, Florida 32533
(850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231 [email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Thursday, August 06, 2009 11:04 AM
To: [email protected]
Subject: RE: water storage tank

Someone designed a water tank and they can't tell you the output? Who sold that 
design contract?


At 11:18 AM 8/6/2009, you wrote:
>I am getting info piecemeal from the engineering firm that is in charge 
>of the tower. They say they don't Know what the residual pressure and 
>flow will be when the tower is completed. We have a sprinkler system 
>going in "next door" to the tower using the existing water from the old 
>system. However, they have installed a 4" pipe with a hydrant instead 
>of 6" (many years ago)and nobody knew until we dug it up.
>
>Now we are flowing 600 gpm through a 4" pipe to our source and the 
>calcs are too close for comfort. We are looking for a "guesstimate"
>of the available water at the base of the tower without any fittings or 
>valves. I can add them in the 8" line from the base to the new tie in 
>point where the systems tie together. We are talking about needing to 
>pick up 5 to 10 psi  not 20 or 30, so as long as we are close we should 
>be good.
>
>This really should fall on the EOR, but as is often the case in this 
>region, if we want to finish the job on time, we have to get an answer 
>immediately.
>
>So I can say that I should reasonably be able to expect .156 x 140'
>= 22 lbs of loss from the tank to the bottom w/o fittings....therefore 
>if we say we should reasonably expect 1,500 gpm at 35 psi?
>
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to