I don't think that no lintel makes it not a bathroom, the code clearly
mentions a bathroom as the occupancy, the lintel is used to separate
areas of larger rooms,ie living room and kitchen or living room and hall
way.

Richard Carr, SET
Design Manager
Associated Sprinkler Co., LLC
336.373.3901 ext 217
[email protected]



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Justin
Reid
Sent: Monday, August 10, 2009 3:08 PM
To: [email protected]
Subject: Definition of Bathroom vs 8 inch lintel

Section 3.3.3 gives the definition of a bathroom and distinguishes
between a
room OR compartment. 8.14.8.1.1 does not require a head in a bathroom
under
55 sf. 3.3.6 Compartment, and 3.3.20 Small Rooms - discuss the
requirement
for an 8 inch lintel to distinguish them from other areas.
I have a room with a toilet in it that is under 55 sf and the sprinkler
head
is omitted from the space. There is a door on this room that is full
height
(i.e. no 8 inch lintel) and 38 inches wide. The door is not self
closing.

It seems to me that the door makes this a room and does not need an 8
inch
lintel to distinguish it as a separate space (room). We have someone
telling
us that it requires the 8 inch lintel or it needs a head in the
bathroom.

Has anyone ran into a similar situation? I have looked for the
definition of
a room and can not find anything so far. Does the door make it a room
regardless of whether it is self closing or full height?

Justin
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)


This email and any attached files are confidential and intended solely for the 
intended recipient(s). If you are not the named recipient you should not read, 
distribute, copy or alter this email. Any views or opinions expressed in this 
email are those of the author and do not represent those of the  company. 
Warning: Although precautions have been taken to make sure no viruses are 
present in this email, the company cannot accept responsibility for any loss or 
damage that arise from the use of this email or attachments.
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to