I spent some time on the web site looking at this and when I saw the 
promotion for greater than the 6.5" bracket, a red flag jumped out. 
Maybe some day they will do some full scale fire tests on cloud 
ceilings and we can figure out what we really need. I know this was 
beyond the post and I hope I didn't confuse anyone.


At 12:34 PM 8/12/2009, you wrote:
>Todd,
>
>Good point but not stated in the original problem. This is a
>problem/benefit we have on the forum when trying to answer questions.
>Sometimes we're led down a tangent that confuses an issue and
>sometimes one that brings up other interesting sidebars. Sometimes I
>wish we would get a little more info from the poster. The actual
>height would have been handy here but then your comment might not have
>been posted and we'd have missed this point. On the other hand
>Monday's residential bathroom question (lintel/full height door) took
>me immediately to 13D since I'm spending most of my residential energy
>these days in attempts to thwart the NAHB's efforts regarding !RC 09.
>
>On Wed, Aug 12, 2009 at 9:02 AM, Todd Williams<[email protected]> wrote:
> > The standard bracket for this product is 6-1/2", which is within
> > Chris' 12". However, the product data also says that they can be hung
> > at any height with standard ceiling wire. So if someone wants to
> > decrease noise in a manufacturing occupancy and installs these 18"
> > down, do we now have a potential cloud ceiling problem beyond Light
> > Hazard occupancies?
> >
> >
> >
> > At 11:40 AM 8/12/2009, you wrote:
> >>You are protecting the floor with sprinklers not the deck.  Ceiling clouds
> >>in themselves are not mentioned in the standard.  The committee in their
> >>infinite wisdom decided 12" is an acceptable distance down for a deflector.
> >>Not counting combustible concealed spaces (which you said this is not) it
> >>doesn't matter what is going on above the sprinklers.  Fly with who, the
> >>AHJ, not a chance they will win this one.  You may choose not to fight if
> >>they give you grief but that doesn't make them right.  I'll turn it around
> >>where does it say you need them above.  Sprinklers are within 12" and then
> >>you treat obstructions in the various zones (<18" and >18").  It's the
> >>obstruction part that drives above and below in typical cloud ceilings.  If
> >>you are at 12" in this case where is the obstruction?
> >>
> >>Chris Cahill, P.E.
> >>Fire Protection Engineer
> >>Sentry Fire Protection, Inc.
> >>
> >>763-658-4483
> >>763-658-4921 fax
> >>
> >>Email: [email protected]
> >>
> >>Mail: P.O. Box 69
> >>         Waverly, MN 55390
> >>
> >>Location: 4439 Hwy 12 SW
> >>               Waverly, MN 55390
> >>
> >>-----Original Message-----
> >>From: [email protected]
> >>[mailto:[email protected]] On Behalf Of Brian Harris
> >>Sent: Wednesday, August 12, 2009 10:20 AM
> >>To: [email protected]
> >>Subject: RE: Armstrong Optima Capz Panels
> >>
> >>Why wouldn't these be treated like ceiling clouds with heads above and
> >>below?  It's open on both sides of the panel (parallel to the joist) to
> >>deck, how can I get away without protecting the deck? I like your idea way
> >>better than mine but I'm not sure it will fly.
> >>
> >>
> >>Brian Harris
> >>FDFP INC.
> >>
> >>-----Original Message-----
> >>From: [email protected]
> >>[mailto:[email protected]] On Behalf Of Chris Cahill
> >>Sent: Wednesday, August 12, 2009 11:09 AM
> >>To: [email protected]
> >>Subject: RE: Armstrong Optima Capz Panels
> >>
> >>I though Jamie answered this Tues. at 2:47 pm.
> >>
> >>"Unobstructed construction? Heads 12" down maybe?"
> >>
> >>That was my thought.  No above and below.  You'll have to see if you can
> >>hide the pipe above, if not exposed.  Arch. will have work with you if
> >>he/she/it wants the pipe covered and you can't fit it above for whatever
> >>reason.
> >>
> >>Chris Cahill, P.E.
> >>Fire Protection Engineer
> >>Sentry Fire Protection, Inc.
> >>
> >>763-658-4483
> >>763-658-4921 fax
> >>
> >>Email: [email protected]
> >>
> >>Mail: P.O. Box 69
> >>         Waverly, MN 55390
> >>
> >>Location: 4439 Hwy 12 SW
> >>               Waverly, MN 55390
> >>
> >>-----Original Message-----
> >>From: [email protected]
> >>[mailto:[email protected]] On Behalf Of Brian Harris
> >>Sent: Wednesday, August 12, 2009 9:56 AM
> >>To: [email protected]
> >>Subject: RE: Armstrong Optima Capz Panels
> >>
> >>Standard school construction, CMU walls, Bar Joist, Metal decking.
> >>
> >>
> >>Brian Harris
> >>FDFP INC.
> >>
> >>-----Original Message-----
> >>From: [email protected]
> >>[mailto:[email protected]] On Behalf Of Seidl Jamie
> >>D.
> >>Sent: Wednesday, August 12, 2009 10:53 AM
> >>To: [email protected]
> >>Subject: RE: Armstrong Optima Capz Panels
> >>
> >>What is your construction type?
> >>
> >>-----Original Message-----
> >>From: [email protected]
> >>[mailto:[email protected]] On Behalf Of Brian Harris
> >>Sent: Wednesday, August 12, 2009 10:33 AM
> >>To: [email protected]
> >>Subject: FW: Armstrong Optima Capz Panels
> >>
> >>Anybody ??
> >>
> >>
> >>Regards,
> >>
> >>Brian Harris
> >>
> >>FDFP INC.
> >>
> >>
> >>
> >>   _____
> >>
> >>From: Brian Harris [mailto:[email protected]]
> >>Sent: Tuesday, August 11, 2009 3:29 PM
> >>To: '[email protected]'
> >>Subject: Armstrong Optima Capz Panels
> >>
> >>
> >>Has anyone ever come across these Armstrong Optima Capz Panels? For product
> >>information you can Google "optima capz". Basically they are an acoustical
> >>panel that are mounted within 6" of the roof deck in an "open" type ceiling
> >>installation. My question is since it is open to deck all around these
> >>panels wouldn't you need heads both above and below the panels? With there
> >>only being 6" max space above these panels and taking into account the top
> >>chord of the joist it only leaves you with 3" or so to run the pipe, add
> >>upright heads, and arm-over's to catch the pendants.......  Is there some
> >>code section that addresses situations like this?
> >>
> >>
> >>Regards,
> >>
> >>                                  <http://www.firstdefensefire.com/>
> >>
> >>
> >>
> >>
> >>
> >>
> >>
> >>
> >>E-mail message checked by Spyware Doctor (6.0.1.441) Database version:
> >>6.13030 http://www.pctools.com/en/spyware-doctor-antivirus/
> >>_______________________________________________
> >>Sprinklerforum mailing list
> >>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>For Technical Assistance, send an email to: [email protected]
> >>
> >>To Unsubscribe, send an email to:[email protected]
> >>(Put the word unsubscribe in the subject field)
> >>
> >>
> >>
> >>
> >>
> >>E-mail message checked by Spyware Doctor (6.0.1.441) Database version:
> >>6.13030 http://www.pctools.com/en/spyware-doctor-antivirus/
> >>
> >>
> >>
> >>
> >>
> >>E-mail message checked by Spyware Doctor (6.0.1.441) Database version:
> >>6.13030 http://www.pctools.com/en/spyware-doctor-antivirus/
> >>_______________________________________________
> >>Sprinklerforum mailing list
> >>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>For Technical Assistance, send an email to: [email protected]
> >>
> >>To Unsubscribe, send an email to:[email protected]
> >>(Put the word unsubscribe in the subject field)
> >>
> >>_______________________________________________
> >>Sprinklerforum mailing list
> >>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>For Technical Assistance, send an email to: [email protected]
> >>
> >>To Unsubscribe, send an email to:[email protected]
> >>(Put the word unsubscribe in the subject field)
> >>
> >>
> >>
> >>
> >>
> >>E-mail message checked by Spyware Doctor (6.0.1.441) Database version:
> >>6.13030 http://www.pctools.com/en/spyware-doctor-antivirus/
> >>
> >>
> >>
> >>
> >>
> >>E-mail message checked by Spyware Doctor (6.0.1.441)
> >>Database version: 6.13030
> >>http://www.pctools.com/en/spyware-doctor-antivirus/
> >>_______________________________________________
> >>Sprinklerforum mailing list
> >>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>For Technical Assistance, send an email to: [email protected]
> >>
> >>To Unsubscribe, send an email to:[email protected]
> >>(Put the word unsubscribe in the subject field)
> >>
> >>_______________________________________________
> >>Sprinklerforum mailing list
> >>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>For Technical Assistance, send an email to: [email protected]
> >>
> >>To Unsubscribe, send an email to:[email protected]
> >>(Put the word unsubscribe in the subject field)
> >
> > Todd G. Williams, PE
> > Fire Protection Design/Consulting
> > Stonington, Connecticut
> > www.fpdc.com
> > 860.535.2080
> > _______________________________________________
> > Sprinklerforum mailing list
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> > For Technical Assistance, send an email to: [email protected]
> >
> > To Unsubscribe, send an email to:[email protected]
> > (Put the word unsubscribe in the subject field)
> >
>
>
>
>--
>Ron Greenman
>Instructor
>Fire Protection Engineering
>Bates Technical College
>Tacoma, WA
>
>Member:
>SFPE, ASCET, NFPA, AFSA, NFSA AFAA
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  