You may need to have an electrical engineer review the installation. 
I did a single phase pump a few years ago and ran into electrical 
problems (for which I was blamed). Hired an EE and he went through 
and found the electrician messed up the installation from the service 
right through to the pump as well as the generator feed and 
connection. Didn't have a converter, but did have two transformers 
because the electrician told us the wrong voltage (208 v. 240 - for 
which I was also blamed).

BTW, what section of the Code says Phase Converters are not allowed? 
I couldn't find that at the time, but had rejected the idea anyway.




At 11:58 AM 8/26/2009, you wrote:
>I need some education of Phase Converters.
>
>
>
>A 300 gpm Fire Pump (Tank fed), is supplied by one of these things. Single
>phase only is available, so one of these has been installed to make it work.
>Installed in '06-07ish, just replaced main board in controller. I was there
>to do test following part replace. 240vac, dropped to 106-108 across the 3
>as indicated on panel. Middle leg showed 422vac in event log, as high peak.
>When started, pump shaft (vertical) jumped up and down repeatedly. We red
>tagged it and are waiting on word from electricians. Pump Motor checked out
>fine. I know they are not allowed, but it was approved, so., I just test it.
>
>
>
>R/
>
>Matt
>
>
>
>Matthew J. Willis, CET
>
>Automatic Fire Sprinklers
>
>Norred Fire Systems L.L.C.
>
>318-387-1134 Voice
>
>318-387-1163 Facsimile
>
>[email protected]
>
>
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to