Todd,

20-A.9.2.2 in the 2007 edition. Not prohibited but not recommended.

On Wed, Aug 26, 2009 at 9:12 AM, Todd Williams<[email protected]> wrote:
> You may need to have an electrical engineer review the installation.
> I did a single phase pump a few years ago and ran into electrical
> problems (for which I was blamed). Hired an EE and he went through
> and found the electrician messed up the installation from the service
> right through to the pump as well as the generator feed and
> connection. Didn't have a converter, but did have two transformers
> because the electrician told us the wrong voltage (208 v. 240 - for
> which I was also blamed).
>
> BTW, what section of the Code says Phase Converters are not allowed?
> I couldn't find that at the time, but had rejected the idea anyway.
>
>
>
>
> At 11:58 AM 8/26/2009, you wrote:
>>I need some education of Phase Converters.
>>
>>
>>
>>A 300 gpm Fire Pump (Tank fed), is supplied by one of these things. Single
>>phase only is available, so one of these has been installed to make it work.
>>Installed in '06-07ish, just replaced main board in controller. I was there
>>to do test following part replace. 240vac, dropped to 106-108 across the 3
>>as indicated on panel. Middle leg showed 422vac in event log, as high peak.
>>When started, pump shaft (vertical) jumped up and down repeatedly. We red
>>tagged it and are waiting on word from electricians. Pump Motor checked out
>>fine. I know they are not allowed, but it was approved, so., I just test it.
>>
>>
>>
>>R/
>>
>>Matt
>>
>>
>>
>>Matthew J. Willis, CET
>>
>>Automatic Fire Sprinklers
>>
>>Norred Fire Systems L.L.C.
>>
>>318-387-1134 Voice
>>
>>318-387-1163 Facsimile
>>
>>[email protected]
>>
>>
>>
>>_______________________________________________
>>Sprinklerforum mailing list
>>[email protected]
>>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, Connecticut
> www.fpdc.com
> 860.535.2080
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to