The biggest single phase fire pump available has a 15 hp motor. Have 
done 3 of them and the power companies have been OK with it.


At 12:33 PM 8/26/2009, you wrote:
>Most utility companies have a maximum Hp they allow for single Ph power,
>locally it is max 10 Hp. Not much advantage to a phase converter if your
>only allowed 10Hp of single phase to supply it. I don't think a converter
>can give you "soft start" capability.
>
>Thom McMahon, SET
>Firetech, Inc.
>2560 Copper Ridge Dr
>P.O. Box 882136
>Steamboat Springs, CO 80488
>Tel:  970-879-7952
>Fax: 970-879-7926
>
>
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of
>[email protected]
>Sent: Wednesday, August 26, 2009 10:30 AM
>To: [email protected]
>Subject: Re: 3 from 1
>
>
>Also, the 2010 edition of NFPA 20 will explicitly state that you cannot
>convert from single to three phase. (according to an NFSA bulletin the
>committee has already agreed on this).
>
>
>
>Forest Wilson
>
>Cherokee Fire
>
>
>-----Original Message-----
>From: Ron Greenman <[email protected]>
>To: [email protected]
>Sent: Wed, Aug 26, 2009 12:26 pm
>Subject: Re: 3 from 1
>
>
>
>
>Todd,
>
>20-A.9.2.2 in the 2007 edition. Not prohibited but not recommended.
>
>On Wed, Aug 26, 2009 at 9:12 AM, Todd Williams<[email protected]> wrote:
> > You may need to have an electrical engineer review the installation.
> > I did a single phase pump a few years ago and ran into electrical
> > problems (for which I was blamed). Hired an EE and he went through and
> > found the electrician messed up the installation from the service
> > right through to the pump as well as the generator feed and
> > connection. Didn't have a converter, but did have two transformers
> > because the electrician told us the wrong voltage (208 v. 240 - for
> > which I was also blamed).
> >
> > BTW, what section of the Code says Phase Converters are not allowed?
> > I couldn't find that at the time, but had rejected the idea anyway.
> >
> >
> >
> >
> > At 11:58 AM 8/26/2009, you wrote:
> >>I need some education of Phase Converters.
> >>
> >>
> >>
> >>A 300 gpm Fire Pump (Tank fed), is supplied by one of these things.
> >>Single phase only is available, so one of these has been installed to make
>it work.
> >>Installed in '06-07ish, just replaced main board in controller. I was
> >>there to do test following part replace. 240vac, dropped to 106-108
> >>across the 3 as indicated on panel. Middle leg showed 422vac in event log,
>as high peak.
> >>When started, pump shaft (vertical) jumped up and down repeatedly. We
> >>red tagged it and are waiting on word from electricians. Pump Motor
> >>checked out fine. I know they are not allowed, but it was approved, so., I
>just test it.
> >>
> >>
> >>
> >>R/
> >>
> >>Matt
> >>
> >>
> >>
> >>Matthew J. Willis, CET
> >>
> >>Automatic Fire Sprinklers
> >>
> >>Norred Fire Systems L.L.C.
> >>
> >>318-387-1134 Voice
> >>
> >>318-387-1163 Facsimile
> >>
> >>[email protected]
> >>
> >>
> >>
> >>_______________________________________________
> >>Sprinklerforum mailing list
> >>[email protected]
> >>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > Todd G. Williams, PE
> > Fire Protection Design/Consulting
> > Stonington, Connecticut
> > www.fpdc.com
> > 860.535.2080
> > ______________________
>_________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
>
>
>
>--
>Ron Greenman
>Instructor
>Fire Protection Engineering
>Bates Technical College
>Tacoma, WA
>
>Member:
>SFPE, ASCET, NFPA, AFSA, NFSA AFAA
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to