True, but when you only have single phase available...? A fire pump
that runs for ten minutes a week if being tested properly (a good bet
that it's not getting proper IT&M if experience is any kind of
teacher) and for a somewhat longer period quarterly, and when and if
there's a fire is certainly cheaper than installing new power lines
from who knows how far away.

On Wed, Aug 26, 2009 at 10:52 AM, Van pellicom Giedo<[email protected]> wrote:
> ...power companies have been OK with it...
>
> Of course thy are ok with it, this small engine EAT ELECTRIC POWER like a
> big one... They like to sell more electricity...
> A 3 phase engine with the same power output will use (if you use correct
> capacitive compensators) about 50 to 75 % of the power that the small engine
> will use.
>
> Giedo
> Belgium friend :-)
>
>
> -----Oorspronkelijk bericht-----
> Van: [email protected]
> [mailto:[email protected]] Namens Todd Williams
> Verzonden: 2009-08-26 19:34
> Aan: [email protected]
> Onderwerp: RE: 3 from 1
>
> The biggest single phase fire pump available has a 15 hp motor. Have
> done 3 of them and the power companies have been OK with it.
>
>
> At 12:33 PM 8/26/2009, you wrote:
>>Most utility companies have a maximum Hp they allow for single Ph power,
>>locally it is max 10 Hp. Not much advantage to a phase converter if your
>>only allowed 10Hp of single phase to supply it. I don't think a converter
>>can give you "soft start" capability.
>>
>>Thom McMahon, SET
>>Firetech, Inc.
>>2560 Copper Ridge Dr
>>P.O. Box 882136
>>Steamboat Springs, CO 80488
>>Tel:  970-879-7952
>>Fax: 970-879-7926
>>
>>
>>
>>-----Original Message-----
>>From: [email protected]
>>[mailto:[email protected]] On Behalf Of
>>[email protected]
>>Sent: Wednesday, August 26, 2009 10:30 AM
>>To: [email protected]
>>Subject: Re: 3 from 1
>>
>>
>>Also, the 2010 edition of NFPA 20 will explicitly state that you cannot
>>convert from single to three phase. (according to an NFSA bulletin the
>>committee has already agreed on this).
>>
>>
>>
>>Forest Wilson
>>
>>Cherokee Fire
>>
>>
>>-----Original Message-----
>>From: Ron Greenman <[email protected]>
>>To: [email protected]
>>Sent: Wed, Aug 26, 2009 12:26 pm
>>Subject: Re: 3 from 1
>>
>>
>>
>>
>>Todd,
>>
>>20-A.9.2.2 in the 2007 edition. Not prohibited but not recommended.
>>
>>On Wed, Aug 26, 2009 at 9:12 AM, Todd Williams<[email protected]> wrote:
>> > You may need to have an electrical engineer review the installation.
>> > I did a single phase pump a few years ago and ran into electrical
>> > problems (for which I was blamed). Hired an EE and he went through and
>> > found the electrician messed up the installation from the service
>> > right through to the pump as well as the generator feed and
>> > connection. Didn't have a converter, but did have two transformers
>> > because the electrician told us the wrong voltage (208 v. 240 - for
>> > which I was also blamed).
>> >
>> > BTW, what section of the Code says Phase Converters are not allowed?
>> > I couldn't find that at the time, but had rejected the idea anyway.
>> >
>> >
>> >
>> >
>> > At 11:58 AM 8/26/2009, you wrote:
>> >>I need some education of Phase Converters.
>> >>
>> >>
>> >>
>> >>A 300 gpm Fire Pump (Tank fed), is supplied by one of these things.
>> >>Single phase only is available, so one of these has been installed to
> make
>>it work.
>> >>Installed in '06-07ish, just replaced main board in controller. I was
>> >>there to do test following part replace. 240vac, dropped to 106-108
>> >>across the 3 as indicated on panel. Middle leg showed 422vac in event
> log,
>>as high peak.
>> >>When started, pump shaft (vertical) jumped up and down repeatedly. We
>> >>red tagged it and are waiting on word from electricians. Pump Motor
>> >>checked out fine. I know they are not allowed, but it was approved, so.,
> I
>>just test it.
>> >>
>> >>
>> >>
>> >>R/
>> >>
>> >>Matt
>> >>
>> >>
>> >>
>> >>Matthew J. Willis, CET
>> >>
>> >>Automatic Fire Sprinklers
>> >>
>> >>Norred Fire Systems L.L.C.
>> >>
>> >>318-387-1134 Voice
>> >>
>> >>318-387-1163 Facsimile
>> >>
>> >>[email protected]
>> >>
>> >>
>> >>
>> >>_______________________________________________
>> >>Sprinklerforum mailing list
>> >>[email protected]
>> >>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> >
>> > Todd G. Williams, PE
>> > Fire Protection Design/Consulting
>> > Stonington, Connecticut
>> > www.fpdc.com
>> > 860.535.2080
>> > ______________________
>>_________________________
>> > Sprinklerforum mailing list
>> > [email protected]
>> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> >
>>
>>
>>
>>--
>>Ron Greenman
>>Instructor
>>Fire Protection Engineering
>>Bates Technical College
>>Tacoma, WA
>>
>>Member:
>>SFPE, ASCET, NFPA, AFSA, NFSA AFAA
>>_______________________________________________
>>Sprinklerforum mailing list
>>[email protected]
>>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>>_______________________________________________
>>Sprinklerforum mailing list
>>[email protected]
>>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>>_______________________________________________
>>Sprinklerforum mailing list
>>[email protected]
>>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, Connecticut
> www.fpdc.com
> 860.535.2080
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to