Well, being an old diesel mechanic, I have a better solution to all this
frequency / voltage stuff...


 
Matthew J. Willis, CET
Automatic Fire Sprinklers
Norred Fire Systems L.L.C.
318-387-1134 Voice
318-387-1163 Facsimile
[email protected]

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Stewart Kidd
Sent: Thursday, August 27, 2009 10:45 AM
To: [email protected]
Subject: Re: 3 from 1

You'd be welcome !

Stewart

PS Bring your voltage and frequency converters - our extra strength  
240v 50 hz AC munches wimpy US 110v 60 Hz appliances !


On 27 Aug 2009, at 16:42, George Church wrote:

> EFSN conference?
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of  
> Matthew J.
> Willis
> Sent: Thursday, August 27, 2009 10:54 AM
> To: [email protected]
> Subject: RE: 3 from 1
>
> Good stuff. Thanks John and all.
>
> I think I need a trip to Europe now...
>
>
> Matthew J. Willis, CET
> Automatic Fire Sprinklers
> Norred Fire Systems L.L.C.
> 318-387-1134 Voice
> 318-387-1163 Facsimile
> [email protected]
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of John  
> Drucker
> Sent: Wednesday, August 26, 2009 11:21 PM
> To: [email protected]
> Subject: RE: 3 from 1
>
> Matt,
>
> Everything you want to know; http://www.convertaphase.com/index.html
>
>
> PS,
>
> While we're on three phase, The "middle leg" is also called the red  
> leg,
> wild leg or high leg. It's usually the B phase in a Three Phase  
> Delta where
> a phase has been center tapped and grounded. This creates a neutral.  
> That's
> helpful because if you need 120 V single phase for something that's  
> how you
> get it. The voltage between Phase A and the neutral will be 120 (208 /
> 1.732) and Phase C to the neutral 120 V.
>
> However if you measure the B phase to the neutral you will find appx  
> 180
> volts on 208 Delta, the wild or high leg ! The high leg, will be  
> marked in
> red or orange. To figure the high leg voltage out take the nominal  
> phase to
> phase voltage, divide by two and multiply by 1.732. (208 / 2 = 104 X  
> 1.732 =
> 180 V on the high leg). Thus the high leg is unusable for single  
> phase power
> yet unsuspecting persons connect 120 V single phase loads from Phase  
> B to
> neutral and soon after smell smoke.
>
>
> Hope that helps
>
> John Drucker, CET
> Fire Protection Subcode Official
> Fire/Building/Electrical Inspector
> Borough of Red Bank, NJ
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of  
> Matthew J.
> Willis
> Sent: Wednesday, August 26, 2009 11:59 AM
> To: [email protected]
> Subject: 3 from 1
>
> I need some education of Phase Converters.
>
>
>
> A 300 gpm Fire Pump (Tank fed), is supplied by one of these things.  
> Single
> phase only is available, so one of these has been installed to make  
> it work.
> Installed in '06-07ish, just replaced main board in controller. I  
> was there
> to do test following part replace. 240vac, dropped to 106-108 across  
> the 3
> as indicated on panel. Middle leg showed 422vac in event log, as  
> high peak.
> When started, pump shaft (vertical) jumped up and down repeatedly.  
> We red
> tagged it and are waiting on word from electricians. Pump Motor  
> checked out
> fine. I know they are not allowed, but it was approved, so., I just  
> test it.
>
>
>
> R/
>
> Matt
>
>
>
> Matthew J. Willis, CET
>
> Automatic Fire Sprinklers
>
> Norred Fire Systems L.L.C.
>
> 318-387-1134 Voice
>
> 318-387-1163 Facsimile
>
> [email protected]
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to