Good stuff. Thanks John and all.

I think I need a trip to Europe now...

 
Matthew J. Willis, CET
Automatic Fire Sprinklers
Norred Fire Systems L.L.C.
318-387-1134 Voice
318-387-1163 Facsimile
[email protected]

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of John Drucker
Sent: Wednesday, August 26, 2009 11:21 PM
To: [email protected]
Subject: RE: 3 from 1

Matt,

Everything you want to know; http://www.convertaphase.com/index.html


PS,

While we're on three phase, The "middle leg" is also called the red leg,
wild leg or high leg. It's usually the B phase in a Three Phase Delta where
a phase has been center tapped and grounded. This creates a neutral. That's
helpful because if you need 120 V single phase for something that's how you
get it. The voltage between Phase A and the neutral will be 120 (208 /
1.732) and Phase C to the neutral 120 V. 

However if you measure the B phase to the neutral you will find appx 180
volts on 208 Delta, the wild or high leg ! The high leg, will be marked in
red or orange. To figure the high leg voltage out take the nominal phase to
phase voltage, divide by two and multiply by 1.732. (208 / 2 = 104 X 1.732 =
180 V on the high leg). Thus the high leg is unusable for single phase power
yet unsuspecting persons connect 120 V single phase loads from Phase B to
neutral and soon after smell smoke.


Hope that helps

John Drucker, CET
Fire Protection Subcode Official 
Fire/Building/Electrical Inspector
Borough of Red Bank, NJ
  

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Matthew J.
Willis
Sent: Wednesday, August 26, 2009 11:59 AM
To: [email protected]
Subject: 3 from 1

I need some education of Phase Converters.

 

A 300 gpm Fire Pump (Tank fed), is supplied by one of these things. Single
phase only is available, so one of these has been installed to make it work.
Installed in '06-07ish, just replaced main board in controller. I was there
to do test following part replace. 240vac, dropped to 106-108 across the 3
as indicated on panel. Middle leg showed 422vac in event log, as high peak.
When started, pump shaft (vertical) jumped up and down repeatedly. We red
tagged it and are waiting on word from electricians. Pump Motor checked out
fine. I know they are not allowed, but it was approved, so., I just test it.

 

R/

Matt

 

Matthew J. Willis, CET

Automatic Fire Sprinklers

Norred Fire Systems L.L.C.

318-387-1134 Voice

318-387-1163 Facsimile

[email protected]

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to