And a height at which it would be tempting to store tables below it, etc. so
protection would be reqd- although leaving 18" clear above the spkrs would
be difficult to enforce past the design phase.

Also, if the church is using real alcohol vrs grape juice, the prev #13
reference asks if flammable liquids are handled above the platform or deck.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jim Johnston
Sent: Tuesday, September 08, 2009 10:51 AM
To: [email protected]
Subject: RE: Church platform

I have done a couple of these both were under 30" off the floor, both had
access panels, and both had lots of wiring under them.  I didn't consider
using 8.15.6, due to the wiring and access panels.

Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
[email protected]

-----Original Message-----
From: Cliff Whitfield [mailto:[email protected]] 
Sent: Tuesday, September 08, 2009 7:34 AM
To: [email protected]; [email protected]
Subject: RE: Church platform

Todd,

 

Would this not fall under 8.15.6 "Spaces under Ground Floors, Exterior
Docks, and Platforms"?  If it met all of the requirements I would think you
could exclude heads under the platform.  Don't forget to apply the 3000 sf
remote area if you elect to not sprinkler that area.

 

Cliff Whitfield, SET

President

Fire Design, Inc.

 

[email protected]

www.fire-design.com

 


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to