And a height at which it would be tempting to store tables below it, etc. so protection would be reqd- although leaving 18" clear above the spkrs would be difficult to enforce past the design phase.
Also, if the church is using real alcohol vrs grape juice, the prev #13 reference asks if flammable liquids are handled above the platform or deck. -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Jim Johnston Sent: Tuesday, September 08, 2009 10:51 AM To: [email protected] Subject: RE: Church platform I have done a couple of these both were under 30" off the floor, both had access panels, and both had lots of wiring under them. I didn't consider using 8.15.6, due to the wiring and access panels. Jim Johnston, P.E. Fire Protection Engineer Inland Fire Protection, Inc 1100 Ahtanum Road Yakima, WA 98903 Phone 509-248-4471 Fax 509-248-1180 [email protected] -----Original Message----- From: Cliff Whitfield [mailto:[email protected]] Sent: Tuesday, September 08, 2009 7:34 AM To: [email protected]; [email protected] Subject: RE: Church platform Todd, Would this not fall under 8.15.6 "Spaces under Ground Floors, Exterior Docks, and Platforms"? If it met all of the requirements I would think you could exclude heads under the platform. Don't forget to apply the 3000 sf remote area if you elect to not sprinkler that area. Cliff Whitfield, SET President Fire Design, Inc. [email protected] www.fire-design.com _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)