Depending on the size of the platform,and the overall size of the project,it may
be more economical to protect below than not,because of the increased pipe
size due to the 3000 sf. design area above if left unprotected.

Lamar Vaughn,SET


---- Thom McMahon <[email protected]> wrote: 
> Where would the "Wind borne debris" come from for an interior platform?
> Crawl spaces loading docks and platforms all could collect wind borne
> debris, but I wouldn't think an interior platform would.
> 
> Yes 11.2.3.1.4 does say when you need to use the 3000 SF design area
> Adjacent  to these areas, but it does not say that the interior platform is
> anything other than a concealed combustible space. 
> 
> Thom McMahon, SET
> Firetech, Inc.
> 2560 Copper Ridge Dr
> P.O. Box 882136
> Steamboat Springs, CO 80488
> Tel:  970-879-7952
> Fax: 970-879-7926
> 
> 
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Cliff
> Whitfield
> Sent: Tuesday, September 08, 2009 11:18 AM
> To: [email protected]
> Subject: RE: Church platform
> 
> Thom,
> 
> I think the platform is intentionally separated with a comma just for that
> purpose.  If you look over in 11.2.3.1.4 "Restrictions" (3) specifically
> addresses both 8.15.1.2 & 8.15.6.  I think it includes interior platforms.
> Not sure why they gave it a separate heading and just didn't include it with
> the concealed space items.
> 
> In reply to an earlier response, I don't think the presence of electrical
> wiring constitutes a need for sprinklers in a space like this but the access
> panels/doors certainly would.
> 
> Cliff
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Thom McMahon
> Sent: Tuesday, September 08, 2009 11:56 AM
> To: [email protected]
> Subject: RE: Church platform
> 
> 8.15.1.1 Concealed Spaces Requiring Sprinkler Protection.
> All concealed spaces enclosed wholly or partly by exposed combustible
> construction shall be protected by sprinklers except in concealed spaces
> where sprinklers are not required to be installed by 8.15.1.2.1 through
> 8.15.1.2.16 and 8.15.6.
> 
> I love where the std can be used to Yeah and Nay at the same time. 
> 
> So where can we use the "Platform" exclusion. I say that this is a question
> for the committee, but my personal position is that we need more info. I
> believe that the "Platform generally referred to is an exterior loading
> platform. I believe that your relying on the comma between the "Exterior
> docks and platforms" Without the comma there is no confusion that the
> platform is also exterior.
> 
> In your case it's an interior platform, so I would say 8.15.1.1 applies.
> What is the construction of this platform? If you build it of "Composite
> wood joist construction" You'd better sprinkler it, or you're looking at a
> 3000 SF design area above and below it. (If there is a below it.) If its
> wood construction of any type and not fire rated, how is it not a concealed
> combustible space?
> 
> 8.15.6.1 Unless the requirements of 8.15.6.2 are met, sprinklers shall be
> installed in spaces under all combustible ground floors, exterior docks, and
> platforms.
> 
> 
> Thom McMahon, SET
> Firetech, Inc.
> 2560 Copper Ridge Dr
> P.O. Box 882136
> Steamboat Springs, CO 80488
> Tel:  970-879-7952
> Fax: 970-879-7926
> 
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of George Church
> Sent: Tuesday, September 08, 2009 8:59 AM
> To: [email protected]
> Subject: RE: Church platform
> 
> And a height at which it would be tempting to store tables below it, etc. so
> protection would be reqd- although leaving 18" clear above the spkrs would
> be difficult to enforce past the design phase.
> 
> Also, if the church is using real alcohol vrs grape juice, the prev #13
> reference asks if flammable liquids are handled above the platform or deck.
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Jim Johnston
> Sent: Tuesday, September 08, 2009 10:51 AM
> To: [email protected]
> Subject: RE: Church platform
> 
> I have done a couple of these both were under 30" off the floor, both had
> access panels, and both had lots of wiring under them.  I didn't consider
> using 8.15.6, due to the wiring and access panels.
> 
> Jim Johnston, P.E.
> Fire Protection Engineer
> Inland Fire Protection, Inc
> 1100 Ahtanum Road
> Yakima, WA 98903
> Phone 509-248-4471
> Fax 509-248-1180
> [email protected]
> 
> -----Original Message-----
> From: Cliff Whitfield [mailto:[email protected]]
> Sent: Tuesday, September 08, 2009 7:34 AM
> To: [email protected]; [email protected]
> Subject: RE: Church platform
> 
> Todd,
> 
>  
> 
> Would this not fall under 8.15.6 "Spaces under Ground Floors, Exterior
> Docks, and Platforms"?  If it met all of the requirements I would think you
> could exclude heads under the platform.  Don't forget to apply the 3000 sf
> remote area if you elect to not sprinkler that area.
> 
>  
> 
> Cliff Whitfield, SET
> 
> President
> 
> Fire Design, Inc.
> 
>  
> 
> [email protected]
> 
> www.fire-design.com
> 
>  
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to