Gentlemen,

A client intents to build a large hall for public transportation.
There are no cars, buses or trains in the hall itself, just plain 
walking area (interchange).
The hall will be protected by dry pipe systems (OH1), because 
freezing can happen inside.
Any shops and commercial booths inside, where storage might occur, 
will all be protected by a wet pipe system (OH2).
The roof of the hall has sky lights, from which we omitted sprinklers 
in compliance with NFPA 13-2007 section 8.6.7 Ceiling Pockets.
The covers of the sky lights are non-plastic. The shops and booths 
have no sky lights.

Initially there were no heat and smoke vents required, but the 
starting-points of design have changed:
Now the sky lights will also be used as heat and smoke vents, because 
the fire marshal requires them.
Moreover, the heat and smoke vents will be triggered by smoke 
detectors and have to open-up before the sprinklers respond.

Question:
Can we still omit sprinklers from the sky lights?
In section 8.6.7 there is no reference to vents.
I know that for the performance of the sprinkler system it is better 
to delay the operation of heat and smoke vents until after the 
sprinklers have responded.

Thank you in advance for sharing your insight.

Frans Stoop
TOS architecture & fire protection
Netherlands
Tel. +31-24-324 0112  

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to