Recent report with detailed sprinkler statistics can be downloaded from NFPAs 
website at:
http://www.nfpa.org/itemDetail.asp?categoryID=521&itemID=18245&URL=Research/Fire%20reports/Fire%20protection%20systems

U.S. Experience with Sprinklers and Other Fire Extinguishing Equipment
John R. Hall, Jr., January 2009. 87 pages.

Geza Szakats 

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of George Church
Sent: Thursday, September 17, 2009 8:34 AM
To: [email protected]
Subject: RE: technical issue

70% of the failures attributable to improperly closed valves is what I
recall, don't know that we hit 97% but it wouldn't surpise me.
I also recall 70% with 2 heads, 90-some% with 4 heads or less controlling
fires. I'd email Jim Lake, staff liason for both 13 and 25- as close to
applicable standards for the study as I can think of.

Sorry to end a sentence with a preposition, Ron.

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Chris Cahill
Sent: Thursday, September 17, 2009 11:15 AM
To: [email protected]
Subject: RE: technical issue

NFPA did a report about 3-5 years ago on the topic of failures.  My summary
is if the valve is open and no one interferes with the system after the fire
starts for all systems the failure rate is very, very tiny like to the
extent it happens but isn't something we need to really worry about.  KEEP
THE DAMN VALVE OPEN!  It's even divided by occupancy.  LH are even smaller
failure rate, storage and high hazard were more but still ridiculously low.
This is the source of George's 70% comment but I don't recall the number.  I
thought it was like 97%.  Or maybe 97% success and of the 3% failure 70% are
from closed valves which leaves 0.9% of all systems would be successful if
the valve was open.  Who ever reads it please remind me.    

They, NFPA, also have save data from what the fire departments report.
That's about the best you can get on that.  And I'll tell you right now even
FD's under report sprinkler saves even when they know about them.  Less
paper work is the motivator here.     

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George Church
Sent: Thursday, September 17, 2009 9:38 AM
To: [email protected]
Subject: RE: technical issue

I'd suggest NFPA as the best source for this. Problem is, there is no
nationwide clearinghouse recording this data like our friends Down Under
have, so many of our "saves" are buried on page 72 of the newspaper, as in
"Sprinkler system floods building" and in the last para they mention- oh,
there was a fire.... but they ignore that the building was saved.

Another source would be FM Global, or other major risk insurers.

I'm trying to recall where I read that 70% of fires spkrs failed to control
were caused by improperly closed valves- NFPA source, don't recall where it
was published, tho. 

Along that line of thought, tho- when PA came out of the early 80's BOCA and
into the I-Codes world in April, 2004, I asked L&I if they were intending to
require compliance with #25 via IBC ref to 13 ref to 25; the answer was that
the intent of the legislature was specifically NOT to require any ITM with
the new Uniform Construction Code based on IBC. (sigh)

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Greg McGahan
Sent: Thursday, September 17, 2009 10:25 AM
To: [email protected]
Subject: technical issue

You guys are great, sometimes abrupt, sometime too silly, but great. I
appreciate and enjoy most of the forum...Thanks,

I need to know if anyone has statistics that show any data related to
sprinkler system failure due to poor maintenance - for a small in house
class I am doing btw.

Thanks for your help. 


Greg McGahan
Operations Manager

Living Water Fire Protection
1160 McKenzie Road
P.O. Box 877
Cantonment, Florida 32533
(850) 937.1850 | Fax (850) 937.1852 | CellĀ (850) 554.3231
[email protected]
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
____________________________________________________________
Electronic mail messages entering and leaving Arup  business
systems are scanned for acceptability of content and viruses

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)