Mike,
Usually the Electrical Inspectors that I have dealt with do not want
sprinkler main piping that runs through the room. If a main is to pass
through then there can be no joints within the space. If a sprinkler head is
to be installed then we pipe it in from outside the room and usually are
required to install a indicating control valve with tamper switch.
G. Tim Stone
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services
117 Old Stage Rd. - Essex Jct., VT. 05452
TEL: (802) 434-2968 Fax: (802) 434-4343
[email protected]
> -----Original Message-----
> From: [email protected] [mailto:sprinklerforum-
> [email protected]] On Behalf Of Brown, Mike
> Sent: Wednesday, October 21, 2009 9:15 AM
> To: [email protected]
> Subject: RE: Water Filled Pipe in Telecomm Room?
>
> Yes, we are providing a sprinkler head for the room.
>
> Mike Brown
> Project Designer
> Sunland Fire Protection
> 1218 Elon Place
> High Point, NC 27263
> Ph. 336.886.7027 Ext. 140
> Fax: 336.886.7024
> WWW.SUNLANDFIRE.COM
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of
> [email protected]
> Sent: Wednesday, October 21, 2009 9:14 AM
> To: [email protected]
> Subject: RE: Water Filled Pipe in Telecomm Room?
>
> Nothing prevents you from running it above the room unless there's some
> military spec saying you can't. NFPA doesn't prevent it. Are you
> providing a sprinkler in the room?
>
>
> Craig L. Prahl, CET
> Fire Protection Specialist
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC 29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> [email protected]
> http://www.ch2m.com
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Brown,
> Mike
> Sent: Wednesday, October 21, 2009 9:10 AM
> To: [email protected]
> Subject: Water Filled Pipe in Telecomm Room?
>
> I working on a design for an existing military barrack... and the FPE
> is
> directing us to run our main through a telecomm room? I am trying to
> find something saying that I can or can't do this? Any thoughts? Thanks
> in advance.
>
>
>
> Mike Brown
>
> Project Designer
>
> Sunland Fire Protection
>
> 1218 Elon Place
>
> High Point, NC 27263
>
> Ph. 336.886.7027 Ext. 140
>
> Fax: 336.886.7024
>
> WWW.SUNLANDFIRE.COM <http://WWW.SUNLANDFIRE.COM>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:Sprinklerforum-
> [email protected]
> (Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]
To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)