In NFPA 70, somewhere. Every electrical inspector I have had will let us enter a room but not exit, with main, branch line, etc. (any piping). I'll try to put my finger on it.
Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 424-0130 office (731) 424-9285 fax (731) 267-4853 cell [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Fletcher, Ron Sent: Wednesday, October 21, 2009 8:30 AM To: [email protected] Subject: RE: Water Filled Pipe in Telecomm Room? Where does it say "not exit electrical rooms"? I know about the restricted space limitations and the required clearances. Ron Fletcher Aero Automatic Phoenix -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Bobby Gillett Sent: Wednesday, October 21, 2009 6:25 AM To: [email protected] Subject: RE: Water Filled Pipe in Telecomm Room? I think what is flagging you is the fact the electrical code causes us to enter and not exit electrical rooms and has restrictions on placement of pipe. You might check with the electrical inspector, or whoever would have that jurisdiction ,and see if it applies to the telecomm room as well. Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 424-0130 office (731) 424-9285 fax (731) 267-4853 cell [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Brown, Mike Sent: Wednesday, October 21, 2009 8:16 AM To: [email protected] Subject: RE: Water Filled Pipe in Telecomm Room? Also, I forgot to mention the telecomm room has no ceiling. Mike Brown Project Designer Sunland Fire Protection 1218 Elon Place High Point, NC 27263 Ph. 336.886.7027 Ext. 140 Fax: 336.886.7024 WWW.SUNLANDFIRE.COM -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of [email protected] Sent: Wednesday, October 21, 2009 9:14 AM To: [email protected] Subject: RE: Water Filled Pipe in Telecomm Room? Nothing prevents you from running it above the room unless there's some military spec saying you can't. NFPA doesn't prevent it. Are you providing a sprinkler in the room? Craig L. Prahl, CET Fire Protection Specialist Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [email protected] http://www.ch2m.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Brown, Mike Sent: Wednesday, October 21, 2009 9:10 AM To: [email protected] Subject: Water Filled Pipe in Telecomm Room? I working on a design for an existing military barrack... and the FPE is directing us to run our main through a telecomm room? I am trying to find something saying that I can or can't do this? Any thoughts? Thanks in advance. Mike Brown Project Designer Sunland Fire Protection 1218 Elon Place High Point, NC 27263 Ph. 336.886.7027 Ext. 140 Fax: 336.886.7024 WWW.SUNLANDFIRE.COM <http://WWW.SUNLANDFIRE.COM> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)