Cliff: Most Tank MFG's have a suction sump option for vert. turbine pumps in fiberglass underground tanks. It's made much like the man-way extension up to ground level the sump extension extends below the bottom of the tank, and saves that extra volume to keep "Submergence" until the tank is empty.
Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 Back on the subject, I learned something invaluable during the NFPA 20 session. Based on the minimum submergence requirement in 7.2.2.2.1 (quoting 07 now) you need quite a bit of water left in the tank to accomplish this. I have never done a Vertical Turbine in an underground tank but you obviously have to oversize the tank to be sure that you compensate for this. Cliff _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)