Cliff: 

Most Tank MFG's have a suction sump option for vert. turbine pumps in
fiberglass underground tanks. It's made much like the man-way extension up
to ground level the sump extension extends below the bottom of the tank, and
saves that extra volume to keep "Submergence" until the tank is empty.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



Back on the subject, I learned something invaluable during the NFPA 20
session.  Based on the minimum submergence requirement in 7.2.2.2.1 (quoting
07 now) you need quite a bit of water left in the tank to accomplish this.
I have never done a Vertical Turbine in an underground tank but you
obviously have to oversize the tank to be sure that you compensate for this.


Cliff