If the oil is not miscible,  good luck with that scheme.  What did the insurer 
use as the basis for that idea?

Typically for oil quenching or dip tanks or similar you would use local app. DC 
or Foam or maybe CO2 depending on conditions and MSDS data.   




Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Fletcher, Ron
Sent: Friday, October 23, 2009 11:45 AM
To: [email protected]
Subject: RE: Report: Antifreeze sprinkler system may have 
contributedtofatalexplosion

It isn't a very thin layer of oil. We are doing 4 fryers that are 6 ft wide by 
18 ft long and hold about 250 gallons of oil at 325F. They run potato chips 
through on a conveyor. I'm not sure but I think the oil is at least 4-6 inches 
deep. I even have a letter from an FM type insurance company confirming the 
water deluge for the fryers.

One of my concerns was amount of free board in the fryers. At about 150 gpm we 
will over flow the free board in a couple minutes. Then everything goes to the 
trench drain.

We priced deluge, LP CO2 and Hifog. Deluge was least expensive, CO2 double the 
cost of deluge and mist was double the cost of CO2. The owner chose deluge.

Ron Fletcher
Aero Automatic
Phoenix, AZ

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Roland Huggins
Sent: Friday, October 23, 2009 7:40 AM
To: [email protected]
Subject: Re: Report: Antifreeze sprinkler system may have 
contributedtofatalexplosion

that's for a flat surface (thin layer of oil) verses a pan of oil (or deep aft 
fryer)

Roland

On Oct 23, 2009, at 5:51 AM, Fletcher, Ron wrote:

> Interesting video. Have you seen FM Data Sheet 7-20 Oil Cookers? It 
> says to put a deluge system discharging at 0.5 gpm per sqft over the 
> hot oil surface.
>
> Ron Fletcher

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to