Hello Craig,

Kitchen hoods procted to NFPA 17A standard are now UL300 and are a wet chemical 
for the appliance protection and have been for a few years. Yes Dry chem is 
still allowed by NFPA 17A for the duct and plenum BUT the manufactures do not 
allow that combo anymore.

Friday, October 23, 2009, 12:01:03 PM, you wrote:

> See that makes no sense.   In kitchen equipment hoods it's usually always 
> some kind of DC or CO2, never water.


> Craig L. Prahl, CET   
> Fire Protection Specialist
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> [email protected]
> http://www.ch2m.com 


> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Fletcher, Ron
> Sent: Friday, October 23, 2009 11:57 AM
> To: [email protected]
> Subject: RE: Report: Antifreeze sprinkler system may 
> havecontributedtofatalexplosion

> It's vegetable oil.

> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of 
> [email protected]
> Sent: Friday, October 23, 2009 8:55 AM
> To: [email protected]
> Subject: RE: Report: Antifreeze sprinkler system may 
> havecontributedtofatalexplosion

> If the oil is not miscible,  good luck with that scheme.  What did the 
> insurer use as the basis for that idea?

> Typically for oil quenching or dip tanks or similar you would use local
> app. DC or Foam or maybe CO2 depending on conditions and MSDS data.   




> Craig L. Prahl, CET   
> Fire Protection Specialist
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> [email protected]
> http://www.ch2m.com 


> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Fletcher, Ron
> Sent: Friday, October 23, 2009 11:45 AM
> To: [email protected]
> Subject: RE: Report: Antifreeze sprinkler system may have 
> contributedtofatalexplosion

> It isn't a very thin layer of oil. We are doing 4 fryers that are 6 ft wide 
> by 18 ft
> long and hold about 250 gallons of oil at 325F. They run potato chips through 
> on a
> conveyor. I'm not sure but I think the oil is at least 4-6 inches deep. I 
> even have a
> letter from an FM type insurance company confirming the water deluge for the 
> fryers.

> One of my concerns was amount of free board in the fryers. At about 150 gpm 
> we will
> over flow the free board in a couple minutes. Then everything goes to the 
> trench drain.

> We priced deluge, LP CO2 and Hifog. Deluge was least expensive, CO2 double 
> the cost of
> deluge and mist was double the cost of CO2. The owner chose deluge.

> Ron Fletcher
> Aero Automatic
> Phoenix, AZ

> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Roland Huggins
> Sent: Friday, October 23, 2009 7:40 AM
> To: [email protected]
> Subject: Re: Report: Antifreeze sprinkler system may have 
> contributedtofatalexplosion

> that's for a flat surface (thin layer of oil) verses a pan of oil (or deep 
> aft fryer)

> Roland

> On Oct 23, 2009, at 5:51 AM, Fletcher, Ron wrote:

>> Interesting video. Have you seen FM Data Sheet 7-20 Oil Cookers? It 
>> says to put a deluge system discharging at 0.5 gpm per sqft over the 
>> hot oil surface.

>> Ron Fletcher

> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

> For Technical Assistance, send an email to: [email protected]

> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)

> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

> For Technical Assistance, send an email to: [email protected]

> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

> For Technical Assistance, send an email to: [email protected]

> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)

> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

> For Technical Assistance, send an email to: [email protected]

> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

> For Technical Assistance, send an email to: [email protected]

> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)



-- 
Best regards,
Charles Thurston
Coastal Fire Protection
 Coastal                            mailto:[email protected]


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to