I think the 16 square feet came from when I was doing research on the
donut fryer and the most flow points I could get over deep fat fryers
(erroneously extrapolating multiple restaurant fat fryer criterion to
industrial cooking equipment) added up to 16 square feet. I may also
not have been too thorough and quit looking when it dawned on me I was
looking for love in the wrong place and the systems were not
appropriate for these applications. And by the way, I believe Tyco was
unable to meet all the criteria of UL300 with the EA-1 (1/4) (the 1/4
being the only EA-1 style listed for commercial cooking) and deleted
the restaurant application cut sheet from the catalogue in November of
1992 (Tyco guys out there for confirmation?). Since UL does not
"un-list" things, systems utilizing EA-1 (1/4) that are still in
service are still listed. I have a couple of brand new (OEM) EA-1
(1/4) manufactured prior to November 1992 if anyone needs them and
wants to make a large contribution to my retirement fund.

On Fri, Oct 23, 2009 at 10:29 PM, David de Vries
<[email protected]> wrote:
> Ron:
>
> You are right about the vegetable oil and high efficiency deep fryer issues 
> that led to the UL 300 standard and predominance of wet chem systems.  17A is 
> the standard for pre-engineered wet chem systems whose application is for the 
> protection of commercial cooking operations.  The pre-engineered part really 
> amounts to what the manufacturer sets as the limit for their system and UL 
> tests to determine that it meets it.  As far as I know, all the mfrs. of wet 
> chem systems focus on typical restaurant appliances, not the large, 
> production cooking equipment that has been the topic of this thread.
>
> As to a hard limit of 16 square feet; I don't think so.  For example, one 
> mfr. has a listed 6 gallon system that can cover 18 flow points.  A nozzle to 
> protect a typical single well deep fryer is 2 flow points, while a typical 
> two to four burner range can be protected with a 1 flow point nozzle.  So, if 
> you had a gang of range tops and protected four burners per nozzle, you could 
> have about 12 four burner range tops of about 4 sq ft each for 48 sq feet of 
> appliances, plus the plenum and duct nozzles, protected by a 6 gallon 
> system.  There are, of course, other limitations like total volume of piping, 
> length of the detection cable, etc. that could further limit the system.  On 
> the other hand, at least one mfr. has an option for ganging cylinders 
> together to cover up to 48 flow points.
>
> Bottom line, if the mfr. does not have instructions that is part of their UL 
> listing for protecting a particular appliance, then a wet chem 17A system is 
> not appropriate, as you pointed out.
>
> Disclaimer:  The above is my opinion only and is not the opinion of NFPA or 
> the Tech Comm on Dry and Wet Extinguishing Systems.
>
>
> Dave
>
> David A. de Vries, P.E., CSP
> Firetech Engineering Incorporated
>
>
>
> --- On Fri, 10/23/09, Ron Greenman <[email protected]> wrote:
>
>
> From: Ron Greenman <[email protected]>
> Subject: Re: Re[2]: Report: Antifreeze sprinkler system may 
> havecontributedtofatalexplosion
> To: [email protected], "Coastal" <[email protected]>
> Date: Friday, October 23, 2009, 8:57 PM
>
>
> Charles,
>
> 17A does not address any dry chem at all but I'll assume you meant 17.
> In truth 17 is merely a dry chem standard and 17A one for wet chem.
> Neither say where they can be used. UL 300 is the listing protocol for
> systems protecting cooking appliances. Cooking lines using only animal
> fats or not having a tilting tray skillet, flat grill or deep fat
> fryer could use dry chem. Only wet chem have been able to meet the
> protocols that include vegetable oils and the described appliances
> above. Since none of these scenarios are likely to occur there is no
> incentive for manufacturers to list anything but wet chem. The big
> issues are the vegetable oil and it's higher auto ignition point and
> the increased insulation on the appliances that delays the cool down
> so much that reflash occurs. As far as I know the largest surface area
> that any wet chem restaurant system is listed for is 16 square feet.
> Kitchen restaurant systems are not appropriate for industrial
> applications under their prescriptive installation manuals. I suppose
> you could have systems engineered with any protection scheme. I once
> did a donut fryer with H-Ex foam that satisfied the fire department.
> Lots of numbers and lots of critical thinking.
>
> On Fri, Oct 23, 2009 at 6:15 PM, Coastal <[email protected]> wrote:
>> Hello Craig,
>>
>> Kitchen hoods procted to NFPA 17A standard are now UL300 and are a wet 
>> chemical for the appliance protection and have been for a few years. Yes Dry 
>> chem is still allowed by NFPA 17A for the duct and plenum BUT the 
>> manufactures do not allow that combo anymore.
>>
>> Friday, October 23, 2009, 12:01:03 PM, you wrote:
>>
>>> See that makes no sense.   In kitchen equipment hoods it's usually always 
>>> some kind of DC or CO2, never water.
>>
>>
>>> Craig L. Prahl, CET
>>> Fire Protection Specialist
>>> Mechanical Department
>>> CH2MHILL
>>> Lockwood Greene
>>> 1500 International Drive
>>> PO Box 491, Spartanburg, SC  29304-0491
>>> Direct - 864.599.4102
>>> Fax - 864.599.8439
>>> [email protected]
>>> http://www.ch2m.com
>>
>>
>>> -----Original Message-----
>>> From: [email protected]
>>> [mailto:[email protected]] On Behalf Of Fletcher, Ron
>>> Sent: Friday, October 23, 2009 11:57 AM
>>> To: [email protected]
>>> Subject: RE: Report: Antifreeze sprinkler system may 
>>> havecontributedtofatalexplosion
>>
>>> It's vegetable oil.
>>
>>> -----Original Message-----
>>> From: [email protected]
>>> [mailto:[email protected]] On Behalf Of 
>>> [email protected]
>>> Sent: Friday, October 23, 2009 8:55 AM
>>> To: [email protected]
>>> Subject: RE: Report: Antifreeze sprinkler system may 
>>> havecontributedtofatalexplosion
>>
>>> If the oil is not miscible,  good luck with that scheme.  What did the 
>>> insurer use as the basis for that idea?
>>
>>> Typically for oil quenching or dip tanks or similar you would use local
>>> app. DC or Foam or maybe CO2 depending on conditions and MSDS data.
>>
>>
>>
>>
>>> Craig L. Prahl, CET
>>> Fire Protection Specialist
>>> Mechanical Department
>>> CH2MHILL
>>> Lockwood Greene
>>> 1500 International Drive
>>> PO Box 491, Spartanburg, SC  29304-0491
>>> Direct - 864.599.4102
>>> Fax - 864.599.8439
>>> [email protected]
>>> http://www.ch2m.com
>>
>>
>>> -----Original Message-----
>>> From: [email protected]
>>> [mailto:[email protected]] On Behalf Of Fletcher, Ron
>>> Sent: Friday, October 23, 2009 11:45 AM
>>> To: [email protected]
>>> Subject: RE: Report: Antifreeze sprinkler system may have 
>>> contributedtofatalexplosion
>>
>>> It isn't a very thin layer of oil. We are doing 4 fryers that are 6 ft wide 
>>> by 18 ft
>>> long and hold about 250 gallons of oil at 325F. They run potato chips 
>>> through on a
>>> conveyor. I'm not sure but I think the oil is at least 4-6 inches deep. I 
>>> even have a
>>> letter from an FM type insurance company confirming the water deluge for 
>>> the fryers.
>>
>>> One of my concerns was amount of free board in the fryers. At about 150 gpm 
>>> we will
>>> over flow the free board in a couple minutes. Then everything goes to the 
>>> trench drain.
>>
>>> We priced deluge, LP CO2 and Hifog. Deluge was least expensive, CO2 double 
>>> the cost of
>>> deluge and mist was double the cost of CO2. The owner chose deluge.
>>
>>> Ron Fletcher
>>> Aero Automatic
>>> Phoenix, AZ
>>
>>> -----Original Message-----
>>> From: [email protected]
>>> [mailto:[email protected]] On Behalf Of Roland 
>>> Huggins
>>> Sent: Friday, October 23, 2009 7:40 AM
>>> To: [email protected]
>>> Subject: Re: Report: Antifreeze sprinkler system may have 
>>> contributedtofatalexplosion
>>
>>> that's for a flat surface (thin layer of oil) verses a pan of oil (or deep 
>>> aft fryer)
>>
>>> Roland
>>
>>> On Oct 23, 2009, at 5:51 AM, Fletcher, Ron wrote:
>>
>>>> Interesting video. Have you seen FM Data Sheet 7-20 Oil Cookers? It
>>>> says to put a deluge system discharging at 0.5 gpm per sqft over the
>>>> hot oil surface.
>>
>>>> Ron Fletcher
>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>>> For Technical Assistance, send an email to: [email protected]
>>
>>> To Unsubscribe, send an email
>>> to:[email protected]
>>> (Put the word unsubscribe in the subject field)
>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>>> For Technical Assistance, send an email to: [email protected]
>>
>>> To Unsubscribe, send an email
>>> to:[email protected]
>>> (Put the word unsubscribe in the subject field)
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>>> For Technical Assistance, send an email to: [email protected]
>>
>>> To Unsubscribe, send an email
>>> to:[email protected]
>>> (Put the word unsubscribe in the subject field)
>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>>> For Technical Assistance, send an email to: [email protected]
>>
>>> To Unsubscribe, send an email to:[email protected]
>>> (Put the word unsubscribe in the subject field)
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>>> For Technical Assistance, send an email to: [email protected]
>>
>>> To Unsubscribe, send an email to:[email protected]
>>> (Put the word unsubscribe in the subject field)
>>
>>
>>
>> --
>> Best regards,
>> Charles Thurston
>> Coastal Fire Protection
>>  Coastal                            mailto:[email protected]
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering
> Bates Technical College
> Tacoma, WA
>
> Member:
> SFPE, ASCET, NFPA, AFSA, NFSA AFAA, WSAFM
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA, WSAFM
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to