Well, everybody here has got it wrong so far. The FM Global rules for velocity in sprinkler systems (there really are none) can be found in Data Sheet 3-0, near the bottom of page 39. Velocity for fire pumps is 15 ft/sec and is found in DS 3-7, page 9, and the velocity for underground mains is 20 ft/sec and is found in DS 3-10, page 8.
-----Original Message----- >From: Todd Williams <[email protected]> >Sent: Oct 27, 2009 2:19 PM >To: [email protected] >Subject: Re: FM's Max. Velocity > >If there is any (and I don't believe so), it is probably 2-8N > > >At 04:00 PM 10/27/2009, you wrote: >>Can someone tell which FM Data sheet talks about the max velocity in a >>wet system? >> >> >> >>Mike Brown >> >>Project Designer >> >>Sunland Fire Protection >> >>1218 Elon Place >> >>High Point, NC 27263 >> >>Ph. 336.886.7027 Ext. 140 >> >>Fax: 336.886.7024 >> >>WWW.SUNLANDFIRE.COM <http://WWW.SUNLANDFIRE.COM> >> >> >> >>_______________________________________________ >>Sprinklerforum mailing list >>[email protected] >>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum >> >>For Technical Assistance, send an email to: [email protected] >> >>To Unsubscribe, send an email to:[email protected] >>(Put the word unsubscribe in the subject field) > >Todd G. Williams, PE >Fire Protection Design/Consulting >Stonington, Connecticut >www.fpdc.com >860.535.2080 >_______________________________________________ >Sprinklerforum mailing list >[email protected] >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > >For Technical Assistance, send an email to: [email protected] > >To Unsubscribe, send an email to:[email protected] >(Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)