>Ken; FM Global dropped velocity requirements for sprinkler systems a quarter 
>century ago.  That would explain why DS 2-8N is silent on the topic.  Remember 
>that DS 2-8N (really FM's footnoted NFPA Standard 13) is just an installation 
>standard, and not a design standard.  It is weak on explaining the concepts on 
>system design.  FM's answer to that weakness was the development of DS 3-0, 
>which was already in place when I joined FM in 1977 and spent 32 years there. 
>
>We'll have to await the release of new DS 2-0 soon to see what commentary is 
>provided on this subject, but I wouldn't expect any real change. 
>
>You might have overlooked the statement "There is no need to use velocity 
>pressure in sprinkler system calculations" in the last paragraph of page 39.
>
>-----Original Message-----
>>From: ParsleyConsulting <[email protected]>
>>Sent: Oct 27, 2009 3:12 PM
>>To: [email protected], Larry Shulman 
>><[email protected]>
>>Subject: Re: FM's Max. Velocity
>>
>>Larry,
>>
>>I'm not sure everybody has it wrong.  I think several people have noted 
>>that there are no longer the limits on velocities in risers, overhead 
>>mains, and branch lines as there were previously.  In looking at the 
>>last copy of 2-8N that I have there is no mention of it as well.
>>
>>The information you referred to in 3-0 on page 39 and subsequently in 40 
>>is not by any stretch a rule for velocity in a sprinkler system, but is 
>>more appropriately described as a means of performing hydraulic 
>>calculations where velocity pressures are taken into account, which is 
>>quite a different matter altogether.
>>
>>Those are just my thoughts.
>>-- 
>>PARSLEY CONSULTING
>>Ken Wagoner, SET
>>760.745.6181 voice
>>760.745.0537 fax
>>[email protected] <mailto:[email protected]> e-mail
>>www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website
>>
>>
>>Larry Shulman wrote:
>>> Well, everybody here has got it wrong so far.  The FM Global rules for 
>>> velocity in sprinkler systems (there really are none) can be found in Data 
>>> Sheet 3-0, near the bottom of page 39.  Velocity for fire pumps is 15 
>>> ft/sec and is found in DS 3-7, page 9, and the velocity for underground 
>>> mains is 20 ft/sec and is found in DS 3-10, page 8.
>>>   
>>>
>>> -----Original Message-----
>>>> From: Todd Williams <[email protected]>
>>>> Sent: Oct 27, 2009 2:19 PM
>>>> To: [email protected]
>>>> Subject: Re: FM's Max. Velocity
>>>>
>>>> If there is any (and I don't believe so), it is probably 2-8N
>>>>
>>>>
>>>> At 04:00 PM 10/27/2009, you wrote:
>>>>     
>>>>> Can someone tell which FM Data sheet talks about the max velocity in a
>>>>> wet system?
>>>>>
>>>>>
>>>>>
>>>>> Mike Brown
>>>>>
>>>>> Project Designer
>>>>>
>>>>> Sunland Fire Protection
>>>>>
>>>>> 1218 Elon Place
>>>>>
>>>>> High Point, NC 27263
>>>>>
>>>>> Ph. 336.886.7027 Ext. 140
>>>>>
>>>>> Fax: 336.886.7024
>>>>>
>>>>> WWW.SUNLANDFIRE.COM <http://WWW.SUNLANDFIRE.COM>
>>>>>
>>>>>
>>>>>
>>>>> _______________________________________________
>>>>> Sprinklerforum mailing list
>>>>> [email protected]
>>>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>>>
>>>>> For Technical Assistance, send an email to: [email protected]
>>>>>
>>>>> To Unsubscribe, send an email to:[email protected]
>>>>> (Put the word unsubscribe in the subject field)
>>>>>       
>>>> Todd G. Williams, PE
>>>> Fire Protection Design/Consulting
>>>> Stonington, Connecticut
>>>> www.fpdc.com
>>>> 860.535.2080  
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>>
>>>> For Technical Assistance, send an email to: [email protected]
>>>>
>>>> To Unsubscribe, send an email to:[email protected]
>>>> (Put the word unsubscribe in the subject field)
>>>>     
>>>
>>>
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>
>>> For Technical Assistance, send an email to: [email protected]
>>>
>>> To Unsubscribe, send an email to:[email protected]
>>> (Put the word unsubscribe in the subject field)
>>>
>>>   
>
>



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to