As Craig reminded me, 2-8N is a thing of the past. If there was any 
requirement, it would be in 3-0. However, what is at the bottom of 
page 39 is velocity pressure, which is different than velocity.



At 05:40 PM 10/27/2009, you wrote:
>Well, everybody here has got it wrong so far.  The FM Global rules 
>for velocity in sprinkler systems (there really are none) can be 
>found in Data Sheet 3-0, near the bottom of page 39.  Velocity for 
>fire pumps is 15 ft/sec and is found in DS 3-7, page 9, and the 
>velocity for underground mains is 20 ft/sec and is found in DS 3-10, page 8.
>
>-----Original Message-----
> >From: Todd Williams <[email protected]>
> >Sent: Oct 27, 2009 2:19 PM
> >To: [email protected]
> >Subject: Re: FM's Max. Velocity
> >
> >If there is any (and I don't believe so), it is probably 2-8N
> >
> >
> >At 04:00 PM 10/27/2009, you wrote:
> >>Can someone tell which FM Data sheet talks about the max velocity in a
> >>wet system?
> >>
> >>
> >>
> >>Mike Brown
> >>
> >>Project Designer
> >>
> >>Sunland Fire Protection
> >>
> >>1218 Elon Place
> >>
> >>High Point, NC 27263
> >>
> >>Ph. 336.886.7027 Ext. 140
> >>
> >>Fax: 336.886.7024
> >>
> >>WWW.SUNLANDFIRE.COM <http://WWW.SUNLANDFIRE.COM>
> >>
> >>
> >>
> >>_______________________________________________
> >>Sprinklerforum mailing list
> >>[email protected]
> >>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>
> >>For Technical Assistance, send an email to: [email protected]
> >>
> >>To Unsubscribe, send an email to:[email protected]
> >>(Put the word unsubscribe in the subject field)
> >
> >Todd G. Williams, PE
> >Fire Protection Design/Consulting
> >Stonington, Connecticut
> >www.fpdc.com
> >860.535.2080
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >For Technical Assistance, send an email to: [email protected]
> >
> >To Unsubscribe, send an email to:[email protected]
> >(Put the word unsubscribe in the subject field)
>
>
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to