Larry,

I'm not sure everybody has it wrong.  I think several people have noted 
that there are no longer the limits on velocities in risers, overhead 
mains, and branch lines as there were previously.  In looking at the 
last copy of 2-8N that I have there is no mention of it as well.

The information you referred to in 3-0 on page 39 and subsequently in 40 
is not by any stretch a rule for velocity in a sprinkler system, but is 
more appropriately described as a means of performing hydraulic 
calculations where velocity pressures are taken into account, which is 
quite a different matter altogether.

Those are just my thoughts.
-- 
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[email protected] <mailto:[email protected]> e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website


Larry Shulman wrote:
> Well, everybody here has got it wrong so far.  The FM Global rules for 
> velocity in sprinkler systems (there really are none) can be found in Data 
> Sheet 3-0, near the bottom of page 39.  Velocity for fire pumps is 15 ft/sec 
> and is found in DS 3-7, page 9, and the velocity for underground mains is 20 
> ft/sec and is found in DS 3-10, page 8.
>   
>
> -----Original Message-----
>> From: Todd Williams <[email protected]>
>> Sent: Oct 27, 2009 2:19 PM
>> To: [email protected]
>> Subject: Re: FM's Max. Velocity
>>
>> If there is any (and I don't believe so), it is probably 2-8N
>>
>>
>> At 04:00 PM 10/27/2009, you wrote:
>>     
>>> Can someone tell which FM Data sheet talks about the max velocity in a
>>> wet system?
>>>
>>>
>>>
>>> Mike Brown
>>>
>>> Project Designer
>>>
>>> Sunland Fire Protection
>>>
>>> 1218 Elon Place
>>>
>>> High Point, NC 27263
>>>
>>> Ph. 336.886.7027 Ext. 140
>>>
>>> Fax: 336.886.7024
>>>
>>> WWW.SUNLANDFIRE.COM <http://WWW.SUNLANDFIRE.COM>
>>>
>>>
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>
>>> For Technical Assistance, send an email to: [email protected]
>>>
>>> To Unsubscribe, send an email to:[email protected]
>>> (Put the word unsubscribe in the subject field)
>>>       
>> Todd G. Williams, PE
>> Fire Protection Design/Consulting
>> Stonington, Connecticut
>> www.fpdc.com
>> 860.535.2080  
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>     
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
>   
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to