Todd,
I'd suggest you install a pressure switch (high/low style) and use it as
your main waterflow alarm like other tank systems do.  Of course that
doesn't help getting water to the head but at least you'd ring and roll the
trucks.  They're listed for this use.
Tom

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Monday, November 02, 2009 11:54 AM
To: [email protected]
Subject: RE: pump failure/flow alarm

Just had another conversation with the fitter. When the IT is opened, 
the paddle goes up for about 3 seconds and then settles back to 
neutral. My guess is that the majority of water is discharged in the 
first few seconds and the pressure pretty quickly dissipates to 
elevation head only and the flow would be only a trickle. At 50 psi, 
a 1/2" sprinkler would discharge 39.6 gpm initially, rapidly 
declining. How long would the 8 gpm need to be maintained for the 
flow switch to activate? The duration of the delay?

The 39.6 gpm translates to 0.66 gallons per second. If that 50 psi 
remained steady, it would take 12 seconds to discharge 8 gallons, 
well under the 30 second setting on the FS. The minimum 8 gpm flow 
requires a 2 psi discharge out of a 1/2" orifice. Will the pressure 
at the orifice drop from 50 psi to 2 psi in 30 seconds in a closed 
system? Probably.

Am I over thinking again?

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to