Might remove the ALV if you've got elec alarms anyway, and a new riser check
might have less friction loss.

Also, calcs that can use a reduced MRA based on lower ceiling height might
help if you change to QR heads.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Wednesday, November 04, 2009 12:14 PM
To: [email protected]
Subject: Re: 1948 Retro

Thanks.  We are chaniging the 3/4" to 1", flushing the entire system, adding
badly needed hangers and probably chaning the alarm and control valve.
-------------- Original message from Todd Williams <[email protected]>:
-------------- 


> Contact Fire Spec in Bridgewater, MA. They would have what you are 
> looking for, if anybody does. I would recommend pulling some of the 
> 3/4 pipe to look for scale. 
> 
> 
> At 11:57 AM 11/4/2009, you wrote: 
> > We are bringing a system up to code that was installed in the 
> > early 1940's. It is a pipe schedule system with 3/4" pipe feeding 
> > the head at the end of each branchline. It is also 51' to the 3rd 
> > floor remote branchline. It is currently 1 lb under the supply 
> > curve using a generic alarm and gate valve for the calculations. 
> > Does any know the friction loss for a 1948 Hodgman Alarm 
> > Valve? What other problems / concerns should I be aware of? 
> >_______________________________________________ 
> >Sprinklerforum mailing list 
> >[email protected] 
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum 
> > 
> >For Technical Assistance, send an email to: [email protected] 
> > 
> >To Unsubscribe, send an email to:[email protected]

> >(Put the word unsubscribe in the subject field) 
> 
> Todd G. Williams, PE 
> Fire Protection Design/Consulting 
> Stonington, Connecticut 
> www.fpdc.com 
> 860.535.2080 
> _______________________________________________ 
> Sprinklerforum mailing list 
> [email protected] 
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum 
> 
> For Technical Assistance, send an email to: [email protected] 
> 
> To Unsubscribe, send an email to:[email protected] 
> (Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)