Just curious.  What triggered the "bringing it up to code"?  There are lots of 
older pipe schedule systems out there that were installed per code at the 
time.  Typically, those would be considered satisfactory unless there was a 
change in use, storage arrangement, etc. that necessitates re-evaluation per 
25, the IFC or other applicable code.

Dave 

David A. de Vries, P.E., CSP 
Firetech Engineering Incorporated 
2715 Harrison St. 
Evanston, IL 60201 
Tel: 847-733-0944 
Fax: 847-866-6255 



--- On Wed, 11/4/09, [email protected] 
<[email protected]> wrote:


From: [email protected] <[email protected]>
Subject: Re: 1948 Retro
To: [email protected]
Date: Wednesday, November 4, 2009, 11:14 AM


Thanks.  We are chaniging the 3/4" to 1", flushing the entire system, adding 
badly needed hangers and probably chaning the alarm and control valve.
-------------- Original message from Todd Williams <[email protected]>: 
-------------- 


> Contact Fire Spec in Bridgewater, MA. They would have what you are 
> looking for, if anybody does. I would recommend pulling some of the 
> 3/4 pipe to look for scale. 
> 
> 
> At 11:57 AM 11/4/2009, you wrote: 
> > We are bringing a system up to code that was installed in the 
> > early 1940's. It is a pipe schedule system with 3/4" pipe feeding 
> > the head at the end of each branchline. It is also 51' to the 3rd 
> > floor remote branchline. It is currently 1 lb under the supply 
> > curve using a generic alarm and gate valve for the calculations. 
> > Does any know the friction loss for a 1948 Hodgman Alarm 
> > Valve? What other problems / concerns should I be aware of? 
> >_______________________________________________ 
> >Sprinklerforum mailing list 
> >[email protected] 
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum 
> > 
> >For Technical Assistance, send an email to: [email protected] 
> > 
> >To Unsubscribe, send an email to:[email protected] 
> >(Put the word unsubscribe in the subject field) 
> 
> Todd G. Williams, PE 
> Fire Protection Design/Consulting 
> Stonington, Connecticut 
> www.fpdc.com 
> 860.535.2080 
> _______________________________________________ 
> Sprinklerforum mailing list 
> [email protected] 
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum 
> 
> For Technical Assistance, send an email to: [email protected] 
> 
> To Unsubscribe, send an email to:[email protected] 
> (Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)