Yes this is a 13R birdcage system that the AHJ is telling us that it is
not allowed.  He stated 8.15.21 as his basis for requiring horizontal
piping on each floor.  Since this reference is out of 13 I didn't think
it applied to a 13R system. 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Cliff
Whitfield
Sent: Tuesday, November 10, 2009 9:03 AM
To: [email protected]
Subject: RE: System subdivision

Dewayne,

I didn't look up the section you mentioned but it sounds like you are
describing a "bird-cage" system.  We used them a lot in 13R in cold
climates to eliminate the need to have any piping in the attic areas
that could be subject to freezing.  You lose the ability to control or
zone the floors but it is sometimes the best approach for the building
owner to keep everything wet and avoid A/F which is more labor intensive
and costly to maintain.

If this is not what you were asking, sorry.

Cliff Whitfield, SET
 
Fire Design, Inc.
3784 Holly Ridge Trail
Marianna, FL 32448
 
Phone: 850-526-1886
Fax:   850-526-1884
Cell:   850-557-1886
 
www.fire-design.com

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dewayne
Martinez
Sent: Tuesday, November 10, 2009 7:58 AM
To: [email protected]
Subject: System subdivision

A) Can section NFPA 13 (07ed) 8.15.21 be applied to NFPA 13R sprinklered
building?

B)Can a multiple floor building, not a high rise, be supplied with
sprinkler piping with the following arrangement and still comply with
section 8.15.21?

    1st floor supplied by horizontal piping with upper floors supplied
by individual rises to sprinklers from 1st floor horizontal piping?

Thanks,

Dewayne Martinez
Design Build Fire Protection
New Berlin, WI
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to