Way too many...about 50...plus they would be above dry wall.  

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Garth W.
Warren
Sent: Tuesday, November 10, 2009 11:16 AM
To: [email protected]
Subject: Re: System subdivision

Could riser control valves be placed on the 1st floor on each "riser" to
aid in impairment requirements or are there way too many "risers"?

Garth

----- Original Message -----
From: "Dewayne Martinez" <[email protected]>
To: <[email protected]>
Sent: Tuesday, November 10, 2009 11:47 AM
Subject: RE: System subdivision


> The section he was referring to in 13 states that "where individual
> floor/zone control valves are not provided, a flanged joint or
> mechanical coupling shall be used at the riser at each floor for
> connections to piping serving floor areas in excess of 5000 SQ FT".
> Since each floor was over 5000 SQ FT, our bird cage system could not
be
> used since we could not isolate the floors in case of system
impairment.
>
>
> Dewayne
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of George
> Church
> Sent: Tuesday, November 10, 2009 10:37 AM
> To: [email protected]
> Subject: RE: System subdivision
>
> I'd ask em where in 13R it says you cannot do the individual risers,
13
> or 13R or 13D. Short of a high rise needing zoning by floor (I think,
we
> don't encounter many) we use them in 13R and d all the time, and also
> did one in a
> 13 hotel, 4-story over parking garage with rental spaces on 1st that
> kicked it out of 13R (as did the garage but since it was subterranean,
> there was a leg to stand on, removed by the rental space not
incidental
> to the residential nature of a hotel).
>
> glc
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Dewayne
> Martinez
> Sent: Tuesday, November 10, 2009 11:21 AM
> To: [email protected]
> Subject: RE: System subdivision
>
> Thanks for all the replies.  I got the same answer back from NFPA that
> 13 applies to 13 not 13R.
> Dewayne
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Joe
> Burtell
> Sent: Tuesday, November 10, 2009 10:04 AM
> To: [email protected]
> Subject: RE: System subdivision
>
> Remind him this is a 13R system and per NFPA 13R 02'
>
> 6.7.2.1 For areas outside the dwelling unit, the following criteria
> shall comply with specifications in NFPA 13, Standard for the
> Installation of Sprinkler Systems, unless permitted by
> 6.7.2.2 and 6.7.2.3:
> (1) Design discharge
> (2) Number of design sprinklers
> (3) Sprinkler coverage
> (4) Position of sprinklers
>
> These are the only 4 things we fall back to NFPA 13 for. There are a
few
> other little things like hangers and EQ bracing but system subdivision
> is not one of them. We have done the bird cage design for years and no
> one has ever said a word.
>
>
> Best regards,
>
> Joe Burtell, SET, CFPS
> Burtell Fire Protection
> Phone: 406.652.7697
> Fax: 406.652.7743
> Cell: 406.861.4507
> Email: [email protected]
> Web Site: http://www.burtellfire.com
> P please don't print this e-mail unless you really need to
>
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Dewayne
> Martinez
> Sent: Tuesday, November 10, 2009 8:40 AM
> To: [email protected]
> Subject: RE: System subdivision
>
> Yes this is a 13R birdcage system that the AHJ is telling us that it
is
> not allowed.  He stated 8.15.21 as his basis for requiring horizontal
> piping on each floor.  Since this reference is out of 13 I didn't
think
> it applied to a 13R system.
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Cliff
> Whitfield
> Sent: Tuesday, November 10, 2009 9:03 AM
> To: [email protected]
> Subject: RE: System subdivision
>
> Dewayne,
>
> I didn't look up the section you mentioned but it sounds like you are
> describing a "bird-cage" system.  We used them a lot in 13R in cold
> climates to eliminate the need to have any piping in the attic areas
> that could be subject to freezing.  You lose the ability to control or
> zone the floors but it is sometimes the best approach for the building
> owner to keep everything wet and avoid A/F which is more labor
intensive
> and costly to maintain.
>
> If this is not what you were asking, sorry.
>
> Cliff Whitfield, SET
>
> Fire Design, Inc.
> 3784 Holly Ridge Trail
> Marianna, FL 32448
>
> Phone: 850-526-1886
> Fax:   850-526-1884
> Cell:   850-557-1886
>
> www.fire-design.com
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Dewayne
> Martinez
> Sent: Tuesday, November 10, 2009 7:58 AM
> To: [email protected]
> Subject: System subdivision
>
> A) Can section NFPA 13 (07ed) 8.15.21 be applied to NFPA 13R
sprinklered
> building?
>
> B)Can a multiple floor building, not a high rise, be supplied with
> sprinkler piping with the following arrangement and still comply with
> section 8.15.21?
>
>    1st floor supplied by horizontal piping with upper floors supplied
> by individual rises to sprinklers from 1st floor horizontal piping?
>
> Thanks,
>
> Dewayne Martinez
> Design Build Fire Protection
> New Berlin, WI
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
to:[email protected]
> (Put the word unsubscribe in the subject field)
> 


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to