It certainly would add to the cost of supervision.

Sent from Jack Leadbetter's
iPhone

On Nov 10, 2009, at 12:16 PM, "Garth W. Warren"  
<[email protected]> wrote:

> Could riser control valves be placed on the 1st floor on each  
> "riser" to aid
> in impairment requirements or are there way too many "risers"?
>
> Garth
>
> ----- Original Message -----
> From: "Dewayne Martinez" <[email protected]>
> To: <[email protected]>
> Sent: Tuesday, November 10, 2009 11:47 AM
> Subject: RE: System subdivision
>
>
>> The section he was referring to in 13 states that "where individual
>> floor/zone control valves are not provided, a flanged joint or
>> mechanical coupling shall be used at the riser at each floor for
>> connections to piping serving floor areas in excess of 5000 SQ FT".
>> Since each floor was over 5000 SQ FT, our bird cage system could  
>> not be
>> used since we could not isolate the floors in case of system  
>> impairment.
>>
>>
>> Dewayne
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of George
>> Church
>> Sent: Tuesday, November 10, 2009 10:37 AM
>> To: [email protected]
>> Subject: RE: System subdivision
>>
>> I'd ask em where in 13R it says you cannot do the individual  
>> risers, 13
>> or 13R or 13D. Short of a high rise needing zoning by floor (I  
>> think, we
>> don't encounter many) we use them in 13R and d all the time, and also
>> did one in a
>> 13 hotel, 4-story over parking garage with rental spaces on 1st that
>> kicked it out of 13R (as did the garage but since it was  
>> subterranean,
>> there was a leg to stand on, removed by the rental space not  
>> incidental
>> to the residential nature of a hotel).
>>
>> glc
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of  
>> Dewayne
>> Martinez
>> Sent: Tuesday, November 10, 2009 11:21 AM
>> To: [email protected]
>> Subject: RE: System subdivision
>>
>> Thanks for all the replies.  I got the same answer back from NFPA  
>> that
>> 13 applies to 13 not 13R.
>> Dewayne
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Joe
>> Burtell
>> Sent: Tuesday, November 10, 2009 10:04 AM
>> To: [email protected]
>> Subject: RE: System subdivision
>>
>> Remind him this is a 13R system and per NFPA 13R 02'
>>
>> 6.7.2.1 For areas outside the dwelling unit, the following criteria
>> shall comply with specifications in NFPA 13, Standard for the
>> Installation of Sprinkler Systems, unless permitted by
>> 6.7.2.2 and 6.7.2.3:
>> (1) Design discharge
>> (2) Number of design sprinklers
>> (3) Sprinkler coverage
>> (4) Position of sprinklers
>>
>> These are the only 4 things we fall back to NFPA 13 for. There are  
>> a few
>> other little things like hangers and EQ bracing but system  
>> subdivision
>> is not one of them. We have done the bird cage design for years and  
>> no
>> one has ever said a word.
>>
>>
>> Best regards,
>>
>> Joe Burtell, SET, CFPS
>> Burtell Fire Protection
>> Phone: 406.652.7697
>> Fax: 406.652.7743
>> Cell: 406.861.4507
>> Email: [email protected]
>> Web Site: http://www.burtellfire.com
>> P please don't print this e-mail unless you really need to
>>
>>
>>
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of  
>> Dewayne
>> Martinez
>> Sent: Tuesday, November 10, 2009 8:40 AM
>> To: [email protected]
>> Subject: RE: System subdivision
>>
>> Yes this is a 13R birdcage system that the AHJ is telling us that  
>> it is
>> not allowed.  He stated 8.15.21 as his basis for requiring horizontal
>> piping on each floor.  Since this reference is out of 13 I didn't  
>> think
>> it applied to a 13R system.
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Cliff
>> Whitfield
>> Sent: Tuesday, November 10, 2009 9:03 AM
>> To: [email protected]
>> Subject: RE: System subdivision
>>
>> Dewayne,
>>
>> I didn't look up the section you mentioned but it sounds like you are
>> describing a "bird-cage" system.  We used them a lot in 13R in cold
>> climates to eliminate the need to have any piping in the attic areas
>> that could be subject to freezing.  You lose the ability to control  
>> or
>> zone the floors but it is sometimes the best approach for the  
>> building
>> owner to keep everything wet and avoid A/F which is more labor  
>> intensive
>> and costly to maintain.
>>
>> If this is not what you were asking, sorry.
>>
>> Cliff Whitfield, SET
>>
>> Fire Design, Inc.
>> 3784 Holly Ridge Trail
>> Marianna, FL 32448
>>
>> Phone: 850-526-1886
>> Fax:   850-526-1884
>> Cell:   850-557-1886
>>
>> www.fire-design.com
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of  
>> Dewayne
>> Martinez
>> Sent: Tuesday, November 10, 2009 7:58 AM
>> To: [email protected]
>> Subject: System subdivision
>>
>> A) Can section NFPA 13 (07ed) 8.15.21 be applied to NFPA 13R  
>> sprinklered
>> building?
>>
>> B)Can a multiple floor building, not a high rise, be supplied with
>> sprinkler piping with the following arrangement and still comply with
>> section 8.15.21?
>>
>>   1st floor supplied by horizontal piping with upper floors supplied
>> by individual rises to sprinklers from 1st floor horizontal piping?
>>
>> Thanks,
>>
>> Dewayne Martinez
>> Design Build Fire Protection
>> New Berlin, WI
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email
>> to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email
>> to:[email protected]
>> (Put the word unsubscribe in the subject field)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email
>> to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email
>> to:[email protected]
>> (Put the word unsubscribe in the subject field)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email
>> to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email
>> to:[email protected]
>> (Put the word unsubscribe in the subject field)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:Sprinklerforum- 
>> [email protected]
>> (Put the word unsubscribe in the subject field)
>>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:Sprinklerforum- 
> [email protected]
> (Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to