They may not necessarily be cars. My garage has a classic boat in it 
and the cars stay outside. The idea of it being a space for 
collectibles so the idea of protecting something of value makes 
sense. That should be addressed directly and specifically with the 
owner, I would think.

He's not thinking about opening a repair garage or some other 
commercial enterprise is he (she)?


At 05:25 PM 11/10/2009, you wrote:
>Ok so you can't make the 15 sec. work. So a dry is out. Antifreeze? If
>someone needs a 7000 sf garage I bet they are not storing rusted out 52
>Desoto. What is the insured value of the cars stored there? Might impact
>your thought process for how to protect them. If he is a car "collector"
>does he also service and work on the cares in this garage? Does he paint
>there? Are cases or drums of oil stored there?
>
>Off the top I'd say that if he doesn't mind losing the cars, then 13D might
>be applicable. If saving the car's is his goal, then I'd look at something
>else.
>
>Thom McMahon, SET
>Firetech, Inc.
>2560 Copper Ridge Dr
>P.O. Box 882136
>Steamboat Springs, CO 80488
>Tel:  970-879-7952
>Fax: 970-879-7926
>
>
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Greg McGahan
>Sent: Tuesday, November 10, 2009 1:53 PM
>To: [email protected]
>Subject: 13D HUGE garage
>
>Under a non-combustible house, 13D, the first floor is slated as a garage of
>7,000 sqft. The owner has requested an add for a dry system to protect the
>garage.
>
>I know some will immediately say that this should be in accordance with 13
>due to the size. I agree that the intent in 13D was probably geared toward
>1-3 cars in a garage and not a dozen or more. However....
>
>The dilemma is this:
>
>Not enough water for a 13 system.
>There is no foreseeable way to get water delivered in 15 seconds per 13D.
>
>I think they would be better off to heat the garage..
>
>Does anyone have definitive info on this issue?
>
>Greg McGahan
>Operations Manager
>
>Living Water Fire Protection
>1160 McKenzie Road
>P.O. Box 877
>Cantonment, Florida 32533
>(850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231
>[email protected]
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to