Are you sure that the apartments will be 13D (not R)? 

13R/D allows for the exclusion of combustible concealed spaces and attic areas. 
If you check on the AFSA website, you can review the 13R code for the exact 
section. 13R is a pretty short document.

Matt Grisé PE*, LEED AP 
Sales Engineer 
Alliance Fire Protection 
*Licensed in KS & MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Karen Purvis
Sent: Wednesday, November 25, 2009 7:52 AM
To: [email protected]
Subject: concealed space

I have checked the archives and can not find what I am looking for. I have
an old school building with an attic area that is not accessible and a 6'
crawl space with no equipment. Building is all wood. They are redoing the
building into apartments (13D). For some reason I remember someone telling
me or reading that in a 13R or 13D system if the areas mentioned were net
being used or accessed then they did not need to be sprinkled. Is this
something I dreamed up?

 

Karen Purvis

Senior Designer

Facility Systems Consultants

713 South Central Street,

Suite 101

Knoxville, TN 37902

ph.865-246-0164

fax 865-246-1084

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to